    Condensing unit too small?



    Hi all, I just wonder what kind of symptoms you might expect to see if the whole condensing unit design is slightly too small to cope with the evaporating unit?

    The system uses R407C and a capilliary tube for throttling.

    I just wanted to see if I'm diagnosing this right. Thanks.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Condensing unit too small?

    I'd imagine long pull down times, high super heat, low evap deltas, thats as much as I can think of right now.

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Condensing unit too small?

    high discharge air temperature from the evaporator and high discharge pressure. low subcooling with high superheat.

  4. #4
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    45
    Posts
    48
    Rep Power
    0

    Re: Condensing unit too small?

    Thanks for your answers, but those are not the symptoms I'm having.

    I'm getting Low Discharge but High suction. Small air temp diff over evaporator and low superheat as if it's overcharged, but the condensing unit came pre-charged and I added no gas. The pipe run is only a couple of meters.

    My guess is the condensing unit is slightly too small, its rated at 18.5KW cooling and the evap unit is rated at 20KW.

    Any ideas?

  5. #5
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Condensing unit too small?

    U mentioned condensing unit and i understood as it is a condenser. so i mentioned to u if the condenser is undersized. However as these symptoms refer to lack of compressor capacity i.e. the compressor has low cooling capacity. The overcharge symptoms are similar to the lack of compressor except the discharge pressure in the case of the compressor inefficiency is low.

  6. #6
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Condensing unit too small?

    Hi

    sounds to me like your not getting a good heat exchange at the evaporator, is the airflow across the evaporator OK?, are the evap fans going the right way? is the coil blocked?

    CB

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Condensing unit too small?

    Hi there,

    Mohamed is completely right.

    When a refrigeration fault occurs LP and HP increase or decrease together. This means is a fault makes the LP to increase so will the HP and vice versa.
    There is only one exception which is lack of compressor capacity. LP and HP act opposite each other. LP increases and HP decreases.
    This is why lack of compressor capacity is the easiest fault to diagnose.

    Cheers
    Even Einstein Asked Questions

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Red face Re: Condensing unit too small?

    suck the gas out and recharge it by weighing the correct amount in,it may be short,it may be that theres a system fault,may even be that the compressors not pumping, i would start there before riping it to bits.

  9. #9
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Condensing unit too small?

    If the condensing unit was to small with respect to the evaporator coil, I would suspect that by the time the system was properly charged so that superheat and subcooling were normal,the suction pressure would be higher than typical.

  10. #10
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Condensing unit too small?

    On second thought, I would say it would act like a fixed metering system under a big load. Normal subcooling, high suction pressure, high superheat

  11. #11
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    45
    Posts
    48
    Rep Power
    0

    Re: Condensing unit too small?

    Wow, thanks for all the comments.

    First, let me just clarify:

    When I say condensing unit, I mean the whole package; Condenser, compressor, fan LP/HP etc as a pre-bought complete unit.

    Second, I've reconsidered and I don't believe the condensing unit is too small and causing these unusual symptoms.

    I believe the capilliary tube is the wrong size/length and is actually flooding the system.

    A number of things lead me to this conclusion:

    1) High suction pressure
    2) Liquid return to compressor and evaporating "late" after leaving evaporator.
    3) Low Discharge pressure. (can't be overcharge)
    4) Warm evaporator.

    I'm going to test this theory out and I will let you know the results.

    Thanks you all again.

  12. #12
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Condensing unit too small?

    You should be able to get the data on the condensing up and cross plot the data wit the evaporator and see where ir should balance.

    I have never trusted precharged units and you need to go back and tweak the charge.

    If they are not grossly mis-matched, it should balance a a slightly higher ET and CT.

    ken

  13. #13
    Chr1s's Avatar
    Chr1s Guest

    Re: Condensing unit too small?

    Have you checked the txv?

  14. #14
    Join Date
    Feb 2007
    Location
    United Kingdom
    Age
    45
    Posts
    48
    Rep Power
    0

    Re: Condensing unit too small?

    Quote Originally Posted by Chr1s View Post
    Have you checked the txv?
    There is no TXV on this system.

    I've checked up on this and the capilliary tube is definately the wrong size. It also seems that there is no actual proven way of calculating the right capilliary size (not that I can find) it's a matter of trial and error.

    So it looks like I'll be doing a lot of testing I might just take the easy route and fit an expansion valve instead.

  15. #15
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Condensing unit too small?

    Quote Originally Posted by carlfoster View Post
    Wow, thanks for all the comments.

    First, let me just clarify:

    When I say condensing unit, I mean the whole package; Condenser, compressor, fan LP/HP etc as a pre-bought complete unit.

    Second, I've reconsidered and I don't believe the condensing unit is too small and causing these unusual symptoms.

    I believe the capilliary tube is the wrong size/length and is actually flooding the system.

    A number of things lead me to this conclusion:

    1) High suction pressure
    2) Liquid return to compressor and evaporating "late" after leaving evaporator.
    3) Low Discharge pressure. (can't be overcharge)
    4) Warm evaporator.

    I'm going to test this theory out and I will let you know the results.

    Thanks you all again.
    Concenring 3 above, don't use the pressure to determine if it is overcharged use the subcooling. I would say in this fixed system if you had in excess of 11C subcooling it is too much charge.

    Low superheat, high subcooling is a fixed metering overcharge.

    You could very well be correct on the wrong metering device, but don't assume it's not over charged based on pressure alone.

Similar Threads

  1. ACC condensing unit 50/60 HZ
    By jan willem in forum Trouble Shooting
    Replies: 7
    Last Post: 07-06-2007, 09:37 PM
  2. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  3. York/Bristol Condensing Unit
    By Abe in forum Commercial
    Replies: 1
    Last Post: 03-02-2003, 07:46 PM
  4. Matching Evaporator with Condensing Unit
    By Abe in forum Technical Discussions
    Replies: 12
    Last Post: 25-07-2001, 08:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •