Results 1 to 5 of 5
  1. #1
    Join Date
    Jun 2007
    Location
    IRAN - ASSALUYEH
    Age
    47
    Posts
    23
    Rep Power
    0

    Question suction line freezeing



    Dear all my co worker.
    thanks for visiting my comment.

    our plant we have the air condition pakage unit(DX type).
    the suction normal operation pressure is 4 bar during the suction line freezes the suction pressure goes down near 1.5 bar and then the suction line be comes freeze.weanwhile the refrigerant of system is enough.
    why the suction line freezes?



  2. #2
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: suction line freezeing

    Hi karimihassan

    Welcome to this forum,

    Ok if the suction line only freezes without the compressor and u mentioned the normal suction pressure is 4 bar and u got 1.5 bar it sounds u have excessive suction pressure drop inside the line causes the suction temperature to drop drastically and makes the frost coating. Each drop in suction pressure 1 bar the temperature drops to 3 K in R-134a. so u have at least 7 to 9 K in AC and most frequently the evaporating temperature of 7.4°C so the suction temperature reaches below zero.

    Does ur system have accumulator ? if yes check it size it may be oversized selection of accumulator.

    Check all the fittings and valves and the suction line design.? more data give more light.

    Cheers

    Mohamed

  3. #3
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: suction line freezeing

    Quote Originally Posted by karimihassan View Post
    Dear all my co worker.
    thanks for visiting my comment.

    our plant we have the air condition pakage unit(DX type).
    the suction normal operation pressure is 4 bar during the suction line freezes the suction pressure goes down near 1.5 bar and then the suction line be comes freeze.weanwhile the refrigerant of system is enough.
    why the suction line freezes?
    What is the on coil and off coil air temperature across the evaporator?
    Probably a plugged air filter or evaporator coil or even a loose fan belt will cause this problem too.

  4. #4
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: suction line freezeing

    Quote Originally Posted by Cofreth View Post
    What is the on coil and off coil air temperature across the evaporator?
    Probably a plugged air filter or evaporator coil or even a loose fan belt will cause this problem too.
    All the prevoius causes the evaportor to frost obvoiusly and then the suction line and the compressor

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: suction line freezeing

    Hi there,

    Measure the superheat and make sure that no liquid is flooding.
    Check the sub-cooling too.

    1- LP low, SH high, SC normal, no temperature drop in liquid line ------------- Lack of expansion device capacity
    2- LP low, SH high, SC normal, temperature drop in liquid line ---------- pre-expansion
    3- LP low, SH high, SC low ------ Lack of refrigerant
    4- LP low, SH low -----------Lack of evaporator capacity

    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Suction line designing for ref. systems
    By Maxim in forum Fundamentals
    Replies: 19
    Last Post: 16-12-2006, 05:43 PM
  3. Measure suction line pressure drop with thermometer
    By Steve Wright in forum Fundamentals
    Replies: 7
    Last Post: 17-09-2005, 11:05 PM
  4. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •