    urgent



    Dear Friends
    It is a pleasure if u can be of any help :
    In some DX air conditioning systems using R134 we face a problem :
    During operation oil is discharged from crank case and then the compressor jams . In reciever sight glass there is thick layer of oil (8 - 10 mm) .
    We came 2 conclusion that the reason is :
    1-Using fake oil or refrigerant ?
    2-As we had the compressors repaired, newly installed oil rings are not working properly so piston sucks oil into chamber and discharges it, as it happens in reciprocating engines causing oil to be burnt.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: urgent

    Is this a newy designed system, or a retrofit of an old r12 air con plant?
    If its a new system is the system designed correctly to allow oil return?
    If it's an old retrofit, then obviously the design is OK, but what oil are you using, how many oil changes did you do?

  3. #3
    Join Date
    Apr 2006
    Location
    phil
    Posts
    5
    Rep Power
    0

    Re: urgent

    please note: oil used in in 134a is different from r12

  4. #4
    Join Date
    Mar 2005
    Location
    Nearby
    Age
    51
    Posts
    22
    Rep Power
    0

    Thumbs up Re: urgent

    With so many thanks.
    Yeap .It is a retrofit cycle but all the procedure in order to change the system has been done correctly.
    Even the oil has been selected appropriately(poly ester)
    But there is something u should know :
    Compressor , Evaporator and condensor are on the same level ( Packaged system )

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: urgent

    Quote Originally Posted by A_Ahed View Post
    With so many thanks.
    Yeap .It is a retrofit cycle but all the procedure in order to change the system has been done correctly.
    Even the oil has been selected appropriately(poly ester)
    But there is something u should know :
    Compressor , Evaporator and condensor are on the same level ( Packaged system )
    What was the original refrigerant? Did you change the TXV?

  6. #6
    Join Date
    Mar 2005
    Location
    Nearby
    Age
    51
    Posts
    22
    Rep Power
    0

    Re: urgent

    Hi
    The original refrigerant was R 12 and we had the TXV changed.

  7. #7
    Join Date
    Nov 2006
    Location
    India
    Posts
    7
    Rep Power
    0

    Re: urgent

    Did you check the cranckcase heater functioning? this seems to be related to flooded start situation. Do you have the pump down cycle?

Similar Threads

  1. urgent
    By Dimitris in forum Trouble Shooting
    Replies: 7
    Last Post: 18-10-2006, 05:55 AM
  2. Urgent G Fault Codes Needed
    By botrous in forum Trouble Shooting
    Replies: 10
    Last Post: 08-08-2005, 08:13 PM
  3. Urgent, Kirchoff question
    By Peter_1 in forum Fundamentals
    Replies: 4
    Last Post: 20-01-2004, 03:12 PM
  4. Urgent!!! S.O.S. - nozzle size
    By herefishy in forum Fundamentals
    Replies: 3
    Last Post: 25-05-2002, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •