    Refrigerant jumping evaporator




    Can anyone explain the problem I'm experiencing with an aged near stuffed Muller evaporator.The system has started icing up the suction line and compressor,when I first saw it I thought easy, frosted evaporator but no such luck.
    The evaporator is frosting at the TX Valve equal frosting over the distributer and first runs on the evaporator and then no more frost until it reappears at a point where the liquid pipe enters the heat exchange section on the suction line, it continues out an ices over the compressor.
    The sight glass shows a great deal of vapour.
    System is running on SP34 drop in with a suction pressure around 170kpa and high side pressure around 750kpa.
    I have tried changing the TX to no avail. Done a leak survey, unable to locate a leak and so i added some refrigerant in an attempt to get a liquid state at the sight glass .
    I can not understand why the system is showing opposite symptoms of vapour in the sight glass and icing the compressor.
    Need to return to the job tomorrow so Id be glad to hear of any suggestions
    Attached Images Attached Images



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Refrigerant jumping evaporator

    I would bet that you have a leak in the heat exchange section. This allows the liquid to enter the suction line without going through the evaporator.
    You probably do not have valves to isolate the heat exchanger, so you might have to cut the liquid line on both sides and pressure test it.

  3. #3
    Join Date
    Jul 2006
    Location
    Copenhagen
    Posts
    39
    Rep Power
    0

    Re: Refrigerant jumping evaporator

    Without a doubt a broken heat exchanger

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Refrigerant jumping evaporator

    Busted heat exchanger for me too.
    Had a tev leak into the equalising line and do something similar, but i see you have replaced this.
    Intersesting condesing unit you have there, makes going to work worthwhile when you find something like this.

    Cheers Jon

  5. #5
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Refrigerant jumping evaporator

    yep ,same hear,try cutting the liquid line pipes off and joining them together,not forgetting to seal the other ends, should do the joby,

  6. #6
    Join Date
    Apr 2006
    Location
    phil
    Posts
    5
    Rep Power
    0

    Re: Refrigerant jumping evaporator

    condition when suction pressure drops too low that frosting occur.Please check if system has no leak considering that Tx valve has been replaced.check if discharge pressure is too high else refrigerant is blocked.
    If disccharge pressure is low and suction pressure is low then possible leak; else lack of refrigerant

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Refrigerant jumping evaporator

    Quote Originally Posted by sylvester View Post
    condition when suction pressure drops too low that frosting occur.Please check if system has no leak considering that Tx valve has been replaced.check if discharge pressure is too high else refrigerant is blocked.
    If disccharge pressure is low and suction pressure is low then possible leak; else lack of refrigerant
    Have you read what's above? NH3LVR was spot on the money, not much liquid in the evap, heaps in the suction line after the evap. Even the OP said liquid was bypassing the evap and that there is in fact a heat exchanger, where the frost line actually starts.

    edit: sorry man, I don't want to bug you on your first post, so don't be too discouraged. I don't want to step on any toes here, but it looks like you replied without reading anything here. The pressures were given in the OP, and everyone's advice here before you was good. Your reply makes no sense here.
    Last edited by paul_h; 29-07-2007 at 03:56 PM. Reason: apology if you get the wrong idea.

  8. #8
    Join Date
    Apr 2002
    Location
    Australia
    Posts
    35
    Rep Power
    0

    Thumbs up Re: Refrigerant jumping evaporator


    Yes you were correct it was hole in the liquid line in the heat exchanger causing the refrigerant to take the easy way back to the compressor.
    I did consider this when I first went to the job but then over analysed the situation thinking what could possibly cause a leak inside the heat exchanger,but thanks to your replies and the shortage of any other possibilites I went ahead with the bypass.
    The patient is now operating within the correct temperature range although as you can see from the back view it really showing its age.
    The butcher is in a rented premise and niether he nor the landlord want to splash out and actually improve the situation it just wire and bailing twine to keep the system limping along.
    Is it just me or does everyone get can't you just fix it , it used to work fine for Grandad.
    Any way thank you very much for your replies it makes it much easier to consider the way others would approach a problem
    Attached Images Attached Images

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Refrigerant jumping evaporator

    Just give it a good therough cleaning and a pat on the back and it'll be fine! I adore thoughs older compressors, I even got one here at home

  10. #10
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Refrigerant jumping evaporator

    Chopped this out today due to the poor quality brazing. thought i'd cut it in half to see how it worked.

    Jon
    Last edited by monkey spanners; 26-09-2007 at 11:16 AM.

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Refrigerant jumping evaporator

    Now that you have cut it apart how are you going to put it back together?
    If all else fails, ask for help.


  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Refrigerant jumping evaporator

    Didn't think of that lol, too late now!

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. Evaporator refrigerant migration
    By Dave the Fridge in forum Trouble Shooting
    Replies: 1
    Last Post: 30-06-2007, 06:31 PM
  4. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  5. refrigerant velocity in evaporator
    By BESC5240 in forum Trouble Shooting
    Replies: 54
    Last Post: 11-07-2005, 12:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •