    Steel galvanized piping with glycols



    Hi Guys,

    Does anobody has been facing some problem using steel galvanized piping with Ethylene or Propylene Glycol?

    Regards,

    Volnei



  2. #2
    Join Date
    Dec 2005
    Location
    Norfolk, England
    Age
    66
    Posts
    132
    Rep Power
    19

    Re: Steel galvanized piping with glycols

    Hi Volnei, We had a system put in with galvanized pipe work some time in the past about 16 to 17 years, It started to rust away on the out side at each joint. The system was running with Mono propylene glycol food grade with an exit temp. of 2oC from the Daikin unit. After about 4 years we removed the galvanized pipe work and fitted Stainless steel SHD 10 grade 304 all welded.
    Arthur

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Steel galvanized piping with glycols

    I do not remember ever seeing galvanized pipe used for glycol. The pipe has always been carbon steel or stainless.
    Last edited by US Iceman; 29-07-2007 at 06:38 PM. Reason: rditing
    If all else fails, ask for help.


  4. #4
    mickmc's Avatar
    mickmc Guest

    Re: Steel galvanized piping with glycols

    Hello all

    Galvinised piping should not be used in a glycol system. After a period of time the glycol can break up and attack the system. The newer Glycols have inhibitors in them to stop attacking the system. glycol should always be mixed with water before adding to system and never added neat.

    mmck

  5. #5
    Join Date
    Aug 2001
    Location
    NE Lincolnshire, UK
    Posts
    145
    Rep Power
    23

    Re: Steel galvanized piping with glycols

    Quote Originally Posted by Volnei View Post
    Hi Guys,

    Does anobody has been facing some problem using steel galvanized piping with Ethylene or Propylene Glycol?

    Regards,

    Volnei
    We had a system on a cold-store floor heater using Mono-ethylene glycol at 30% mix. The headers were steel but the pipes in the floor were polypropylene.

    Even with corrosion inhibitors, it still seemed to attack the steel where it leaked out. The galvanising was OK where there was no damage, but any threaded joints or where the galv was damaged suffered.

    If the system could be installed with no risk of mechanical damage, I'd look at plastic pipes as a possible alternative if I was putting a new system in.

    Steve

Similar Threads

  1. Cutting through Stainless Steel
    By Abe in forum Air Conditioning
    Replies: 14
    Last Post: 14-06-2009, 03:57 AM
  2. Stainless Steel Evaporators
    By Electrocoolman in forum Commercial
    Replies: 6
    Last Post: 18-10-2006, 10:29 PM
  3. Stainless steel insead of carbon steel
    By torque in forum Industrial
    Replies: 2
    Last Post: 23-09-2003, 09:45 PM
  4. Evaporators: Stainless Steel or Galvanized S.
    By Friobernal in forum Technical Discussions
    Replies: 2
    Last Post: 28-10-2002, 09:04 PM
  5. titanium and copper/brass/or stainless steel brazing?
    By vinay in forum Trouble Shooting
    Replies: 4
    Last Post: 08-08-2002, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •