25-07-2007, 11:45 PM #1
Daikin twin split
Does anyone know the dip switch settings for a daikin skyair twin split ? Someone prior to myself has decommissioned a twin split to be re-installed within the same building at a different level . On re-commissioning we have a UA fault ???? Too many evaps .... would appear to me that the dip switches may have been fiddled with or accidentally changed during storage. Any help gratefully appreciated .
-
26-07-2007, 12:01 AM #2
Re: Daikin twin split
If you give me the model number I can find out for you.
Otherwise, if you go to www.daikin.co.uk you are able to download the manual (but again, you will need the mod no)
-
28-07-2007, 06:28 PM #3
Re: Daikin twin split
Problem solved , the installer added an extra cable to P1 & P2 which weren't required.