Results 1 to 8 of 8
  1. #1
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Dunham Bush Chiller Fault Codes



    Does anyone have any fault codes for Dunham Bush Chillers. Its a bit of an old one (1996) No ongoing maintenance and a bit of a mess. Two Refcomp recips and total capacity I think 415kW.

    Three codes show on the history 10, 19 and 26. No OEM manuals anywhere either, so relying on some outside help.

    Thanks


    a problem shared is a problem halved

  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes


  3. #3
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes

    Thanks for the link, but this chiller will have the old MP2000 control panel and gives nothing other than 2 digit codes for errors.
    Cheers
    a problem shared is a problem halved

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes


  5. #5
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes

    Looks like I might have to try and contact Dunham Bush. But Thanks for the attempts anyway. Very much appreciated.
    a problem shared is a problem halved

  6. #6
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes

    No problem!

  7. #7
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Dunham Bush Chiller Fault Codes

    Perhaps I can help more, but I can't remember what the MP2000 looks like in the front (display)! Perhaps than I can find the correct manual (paper) here at home!

  8. #8
    Join Date
    Aug 2001
    Location
    Havant, Hampshire, UK
    Posts
    12
    Rep Power
    0

    Re: Dunham Bush Chiller Fault Codes

    If your unit does have a Mp2000 controller, then go to the Digital menu. Enter, and then scroll down until the number corresponds with your alarm code. i.e digital 10 may say something like Oil Pressure Switch circuit 1. This will tell you a oil failure problem on that circuit. Hope that is clear..

Similar Threads

  1. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  2. carrier chiller fault codes
    By al in forum Air Conditioning
    Replies: 7
    Last Post: 20-07-2009, 10:10 PM
  3. Dunham Bush Chiller
    By iceman007 in forum Air Conditioning
    Replies: 5
    Last Post: 10-05-2007, 06:57 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •