Results 1 to 19 of 19
    44
    3,800
    38
    Oh the horror!!!
    Got asked to look at a couple of coldrooms installed 4 months ago that have been giving trouble......
    Second hand stuff, 3 months warranty.....
    Heres a list of what i've found so far.
    coldroom 1
    Panel upsidedown, 20mm hole in bottom of panel, 3x20mm holes in top of panel, incomming swa cable no gland just stuffed through hole, 2 incomming syy cables not made off just stuffed through hole, panel full of water due to holes shorted out compressor 3ph breaker and contactor, main switch cracked, 1994 vintage R12/R22/R502 unit running on R404A, old mineral oil visible in sightglass, syy cable not made off earthed in evaporator, no clips on the pipework, no isolators on the condensing unit, no solenoid valve, 053 drier seems a bit small for field built system (2hp unit), no labeling of refrigerant type/weight, 20mm hole into comp lecky box,
    coldroom 2
    repeat of above plus 4 extra hole in bottom of panel, 32a breaker running 2.5mm cable to comp (6a load), leaky comp oil sightglass, leaky rotalock valve on reciever, compressor fault/ seized, R404A with mineral oil.
    While you are here......
    coldroom 3
    would not get below 14c, should be 4c. Found defrost heater wired to permanent live no stat, it was only the unit running that stopped it catching fire, drier in backwards, no isolator, fan catching on condenser and blade bent, internal tev with distributor, hole in the bottom of control panel the size of a letter box.
    The installing company have supplied a Hammerite rebuild compressor to replace the duff one.
    I'm sure there is more to come.....
    Cheers Jon
    44
    3,800
    38
    Re: Oh the horror!!!
    And...
    Cheers Jon
    Oct 2001
    Nottingham UK
    5,127
    42
    Nice Job
    I really like the bends in the suction line to the cond unit - and then the liquid line just trawls across the floor
    10/10 for trying.
    I'm back on the Pale
    Aug 2005
    5,327
    An aptly named thread.
    It's always nice to see someone take pride in their workmanship.
    Aug 2003
    Netherlands
    43
    621
    15
    Must have read somewhere that 404 is a drop in for R22 and thought, just drop it in!
    Feb 2007
    France now, Suffolk before
    49
    294
    12
    Oh, beauty though art fled to brutish beasts and men hath lost their reason.
    William you know who!
    70
    10,627
    52
    There's another of those condensing units with carrying handles
    Mind you the location of that condensing unit appears to have been a site measured position as in
    - Where do want this mister?
    - Just put it down there mate.
    - OK
    - Fitter comes along and pipes it up before anyone can change their mind.
    It's the little things..... there are three holes in the panel already so they drill three new ones - DOH!
    70
    10,627
    52
    On second thoughts - I think I'll go with Franks' install from earlier.
    Feb 2007
    2,477
    Why do you lot keep following me around?
    Jan 2003
    Crewe, United Kingdom
    52
    726
    So? Whats wrong with it?
    Karl
    Aug 2005
    Brisbane australia
    66
    34
    Some people are just PICKY, PICKY PICKY!!!
    44
    3,800
    38
    Swapped the compressor for the "rebuilt" one and found this green stuff in the suction valve and filter.
    Oil sight glass was leaky but luckily i had a spare o ring for it. Changed the oil to ester. while looking into the sump the bottom of the sump was rusty coloured copper plating? Final pic is my oil changing device Also system had no gas left in it, leak on reciever conection.
    Cheers Jon
    Oct 2006
    1,848
    15
    Cheers Jon
    Looks like it was built to last eh?
    Cheers taz
    44
    3,800
    38
    Some pics of the duff compressor, thrown a rod or two and cooked the windings
    Mar 2005
    71
    639
    14
    Some people are sure pickey about scab work.
    Ken
    May 2009
    New Zealand
    40
    Ah, this beauty reminds me of a "BLAST" frezzer I went to once. Pretty similar install standards. But my one had part winding start, and you guess it it was running on 2 thirds of its windings, with every one unsure as to why it it couldnt get a sst below -20degc. Got to love that 3 month partial warranty (Yeah Not That Part)
    Apr 2010
    45
    297
    9
    i think yr being real picky lmao it is bad unfortunately i have seen alot worse lets hope they failed there F gas an cant do any more work did the guy say wot he paid for job ? that usually defines the quality
    44
    3,800
    38
    Recently replaced one of the systems due to the evap rotting out from fumes from the cheese stored in it,
    http://www.youtube.com/watch?v=pSBr5qB5OPk
    Jon
  19. #19
    Dec 2009
    uk
    13
    unbeleivable!! makes a mokery of the industry,they should be imprisoned