    freezer cold room pull down slow



    30 hp bitzer unit coldroom temp required -20
    new system suction 20 psi discharge225 psi
    sight glass clear , frosting back to compressor
    pipe run is25 m , evaporator temp -16
    have changed valve ,same problem this is on r404
    any idea out there nick on behalf of jason



  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: freezer cold room pull down slow

    Quote Originally Posted by nick clark View Post
    30 hp bitzer unit coldroom temp required -20
    new system suction 20 psi discharge225 psi
    sight glass clear , frosting back to compressor
    pipe run is25 m , evaporator temp -16
    have changed valve ,same problem this is on r404
    any idea out there nick on behalf of jason

    At 20psi suction and frosting back on the suction line I would sugest you measure the superheat and pherhaps you could open your valve a bit.
    At 20psi the refrigerant is evaporating at about -35deg C.
    The frost on the suction could be cold gas returning and not liquid.
    Check the superheat settings and set the valve up if required.
    You could allow your back pressure to rise to 2b (30psi) and still freeze the room correctly.

    Cheers taz.

  3. #3
    Join Date
    Jul 2006
    Location
    uk
    Posts
    11
    Rep Power
    0

    Smile Re: freezer cold room pull down slow

    many thanks , will pass on info to jason , he also told me there is no heat x fitted , i feel this would help ?
    nick

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: freezer cold room pull down slow

    Hi nick clark,

    Has the selection of the equipments and the controls been done properly. As I am very much involved in such projects, I have seen a small mistake makes a lot of difference in refrigeration.

    Please recheck the equipments and the selection of the TEV.

  5. #5
    Join Date
    Jul 2006
    Location
    uk
    Posts
    11
    Rep Power
    0

    Unhappy Re: freezer cold room pull down slow

    yes ,same set up used before on coldroom same size
    regards nick

  6. #6
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: freezer cold room pull down slow

    Quote Originally Posted by nick clark View Post
    yes ,same set up used before on coldroom same size
    regards nick
    May be a defective TEV

    Suny

  7. #7
    Join Date
    Jul 2006
    Location
    uk
    Posts
    11
    Rep Power
    0

    Re: freezer cold room pull down slow

    hi suny , changed tev just the same nick

  8. #8
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: freezer cold room pull down slow

    An error may give you big problem. Did you top up with R 404a. If so you will have this problem. Then reclaim & chrage again with fresh gas.

    Suny

  9. #9
    Join Date
    Jul 2006
    Location
    uk
    Posts
    11
    Rep Power
    0

    Unhappy Re: freezer cold room pull down slow

    hi suny large plant so pump down to change valve
    no loss of refrigerant nick

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: freezer cold room pull down slow

    Quote Originally Posted by nick clark View Post
    yes ,same set up used before on coldroom same size
    regards nick
    It means of assessing the load, you have just copied the the equipments from a similar Cold Room. This is a dangerous thing to do. In refrigeration, I always every project as a new one and do all the calculations in details. Even the selection of equipments and controls. In this way, God willing I never had any problem in attaining the temperatutre nor the pull down period.

    Please do recheck the compressor, condenser and the evaporators and of course the TEV and the pipe lines.

    If I could be of any help, please do let me know.

  11. #11
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: freezer cold room pull down slow

    Please check the product load. Maybe it is quite different from the previous one.

Similar Threads

  1. Misa Kit Freezer Room
    By Abe in forum Commercial
    Replies: 2
    Last Post: 03-01-2007, 09:04 PM
  2. LG Capacitor - Room not cold
    By kelamel in forum Trouble Shooting
    Replies: 8
    Last Post: 21-10-2006, 10:50 AM
  3. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM
  4. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •