    I've been working on a 15 ton split chiller and the unit doesn't seem to be piped correctly in my eyes. The Unit has a plate heat exchanger that has the TXV entering the bottom of the exchanger. I was thinking two ways of this, one pro, one con. The pro side is, this would force any liquid to boil in order to escape its own gravity, thereby protecting the compressor. The con is, the oil would most likely want to log in the bottom of the exchanger. I've seen many manuals showing the entry on the top OR bottom. I'm just not sure if one was reversed just for diagram purposes. Does anyone know if there is a hard and fast rule about this???
    My wife says I don't listen to her....or something like that....
    May 2002
    TN
    124
    23
    A system with the evap piped from the top should have a liquid line soleniod and a pump-down cycle. Many medium temp systems are piped from the top without a LL soleniod. Does not seem like the best way to protect the compressor. Evap is typically the coolest place. All the ***** will migrate to the evap in the off cycle. When the compressor starts, it could get a shot of liquid.
    Aug 2001
    Leominster, MA
    71
    45
    Cool proper piping techniques
    If you'll notice, I said the evaporator was piped from the BOTTOM, not the top! In most cases, even the TXV will slam shut and prevent the refrigerant from getting into the low side, but I do agree the LL solenoid is always a cheap insurance plan.
  1. Pressure piping test
    By Volnei in forum Industrial
    Last Post: 03-07-2010, 10:30 PM
  2. HVAC piping design software
    By NoNickName in forum Fundamentals
    Last Post: 06-02-2010, 06:29 AM
  3. Name of old refrigeration technique
    By Guy Burns in forum Chit Chat & Service Stories
    Last Post: 18-08-2006, 04:25 AM
  4. Piping Advice
    By Mickvee in forum Air Conditioning
    Last Post: 11-06-2006, 03:39 PM
  5. Vibration in refrigerant piping
    By US Iceman in forum Technical Discussions
    Last Post: 01-05-2006, 11:53 PM