    Expantion Valve Freeze Over



    What are the main reason for the expantion valve freezing over in a free standing Fosters comercial fridge?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Expantion Valve Freeze Over

    Could be a blockage at the valve, a shortage of refrigerant due to a leak or a failure of the valve.

    All this is assuming that the airflow over the evaporator is correct and that the defrost system is operating correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    tommy658's Avatar
    tommy658 Guest

    Re: Expantion Valve Freeze Over

    Thanks for the advise. The refrigerant level and air flow are all fine. Whats the best way to test if the valve in faulty?

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Expantion Valve Freeze Over

    How can you be sure the refrigerant charge is in order?

    If it's working ok and the expansion valve is frosting there doesn't have to be a problem! It can also be caused by bad or no isolation on the outgoing side of the valve. For sure if the temperature is low enough compared to the surounding are and it's moisture level!

  5. #5
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Expantion Valve Freeze Over

    Is the door seal OK, it could be warm air getting in.

    Ian

  6. #6
    Join Date
    May 2006
    Location
    scotland
    Posts
    31
    Rep Power
    0

    Re: Expantion Valve Freeze Over

    Hi Tommy,

    Reading between the lines here and correct me if im wrong, im going to assume that the fridge in question isnt working and the exp valve is frosting over and you want to know if this is normal, and if not, what can cause this.
    In my experience of working on any integral with an exp valve fitted is, that if you suspect the valve of being clogged it will frost over but you can crack both flare nuts on either side of valve to check. No liquid, system has refrigerant problem. Liquid at inlet no liquid at outlet, faulty valve. This only works as a last resort and you have exhausted all other means of cause, and of course it stops an engineer from guessing.

    kind regards

    alex

    P.S
    If its an older foster cabinet and has had the compressor replaced on it at some point and its still the origional exp valve, it may very well be clogged.

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Expantion Valve Freeze Over

    Hi tommy 658,

    You have not stated as what is the status of the unit. Is it working and maintaining the desired conditions.

  8. #8
    tommy658's Avatar
    tommy658 Guest

    Re: Expantion Valve Freeze Over

    The system runs fine at 1-4 degrees but then after a few days it strugles to pull down below 8. Each time I check it the valve is frozen over and Ihave to manually defrost it then its ok again. The fridge is opened frequently and is in a hot galley. I have opened the valve 1/2 a turn and it works for longer but still has to be shut down and defrosted every 10 days. I have 5 units in total and its only happening to 1 of them.

  9. #9
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Talking Re: Expantion Valve Freeze Over

    i trust its had a new drier ?,i would pump it down and change it,valve as well ,running back and forth must be costing someone, is it off cycle defrost or heaters ?the coil may be getting sufficient heat to defrost but the shear material mass of the valve may not,you could try wraping it with armaflex tape or mess about with the defrost times to achive this. somewhere to start anyway.bit awkward when you cant see it

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Expantion Valve Freeze Over

    As per Old Gas Bottles suggestion, please change the drier and the Expansion Valve. In the case of the Expansion Valve, ensure that the selection is proper. Which make and model is the Expansion Valve ?

  11. #11
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: Expantion Valve Freeze Over

    As posted earlier,It could be an obstruction in the valve or moisture in the systen.Moisture in the system would cause the txv to ice at the orfice blocking flow.

  12. #12
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Expantion Valve Freeze Over

    Hi unit is short of gas if tev is iced up after a few days regards phil

Similar Threads

  1. FRICK TDSH 233 Slide Valve and guide damaged
    By 404cab in forum Industrial Compressors
    Replies: 9
    Last Post: 30-07-2008, 11:24 PM
  2. Expantion valve adjustment
    By ayaz in forum Technical Speculations
    Replies: 5
    Last Post: 22-04-2006, 03:43 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •