    Estimation of Gas charge for Screw Chillers



    Dear Members,

    Normally we select the refrigerant charge quantity for screw chillers by mass flow rate per ton and then fine tuning it during test.

    Whether there is any other way of estimating it which is closer and accurate to the requirement?

    Cheers!



  2. #2
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Estimation of Gas charge for Screw Chillers

    By knowing the absolute suction pressure, enter P-h chart or calculator u can get the refrigerating effect, hfg ((kJ/(kg.K)) or latent heat (vapor enthalpy - liquid enthalpy). Thus:

    minimum mass flow rate = (tons of refrig.*3.517)/Latent heat(kJ/(kg.K)) = ---- kg/s

    the product is the minimum mass flow rate and if u want to know also the actual but approximetly by this:

    normally the inlet refrigerant dryness fraction to the evaporator (Dx coil but others = 0) = 0.2 to 0.25


    Mass flow rate = (tons of refrig.*3.517)/((1- 0.2 or 0.25)* Latent heat(kJ/(kg.K)*1.05) = ---- kg/s

    the figure 1.05 accounts for the effect of superheating load.

    this is method is valid for any refrigeration application screw or scroll or recp...

    Cheers

  3. #3
    Join Date
    Jun 2007
    Location
    In India
    Age
    52
    Posts
    33
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    Dear Mohamed,

    Thanks for your reply. Your reply gives the estimation of mass flow rate. Can we also estimate the charge quantity in Kg or any other unit.

    I know that this will be tricky thing as it depends on condenser and cooler and other accessories.

    Any specific guidelines?

    Best regards,

  4. #4
    Join Date
    Jul 2007
    Location
    São Paulo
    Posts
    11
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    tadipatrir,

    It is not so accurate , but help imediatelly:

    I use 0.8Kg per Ton of Refrig. I use this calc only for R22

    cheers!

  5. #5
    Join Date
    Jun 2007
    Location
    In India
    Age
    52
    Posts
    33
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    Dear Dalmo,

    Thanks for the reply.

    Any such thumb rule for R134a refrigerant?

    Regards,

  6. #6
    Join Date
    Jun 2007
    Location
    In India
    Age
    52
    Posts
    33
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    Dear Dalmo,

    Thanks for the reply.

    Any such thumb rule for R134a Refrigerant?

    Regards,

  7. #7
    Join Date
    Jul 2007
    Location
    São Paulo
    Posts
    11
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    tadipatrir,


    I use for 134a 1.0 kg per ton, It's not accurate again, but it is better has a little more gas recipes to charge . Maybe you try to be able to find a tecnicall bulletin of you Screw Chiller knowing the right charge!

    cheers!
    post scriptum:

    excuse for reply, because the GMT!

  8. #8
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: Estimation of Gas charge for Screw Chillers

    There are so many variables anything posted would just be a guess. The above estimates are accurate for the situations that the individual posters are experiencing.

    Ive seen 250 ton R22 packaged screws with 1000HP motors running -20 evap holding 7000#s of refrigerant.

    On the other end of the spectrum I've seen 250 ton packaged R22 screws with 40F evaps using 600#s of gas.

    If you have piping to add and the unit is other than a packaged skid, your charge could be anywheres from 2#s per ton to the skies the limit. JMHO

  9. #9
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Estimation of Gas charge for Screw Chillers

    If u multipy the prevoius equations that i have posted earily to RPS u can get easily the mass kg i.e.

    Mass (kg)= (tons of refrig.*3.517)/((1- 0.2 or 0.25)* Latent heat(kJ/(kg.K)*1.05)*RPS

    RPS = compressor rotational speed in revoltion per second. Otherwise u use the roughly estimation of "Dalmo" gave. I wish it could help

    Best regards

Similar Threads

  1. Help please. How to charge a unit
    By God55 in forum Air Conditioning
    Replies: 18
    Last Post: 23-03-2007, 10:07 AM
  2. Subcooling vs charge graph?
    By Larry2 in forum Fundamentals
    Replies: 4
    Last Post: 01-12-2006, 07:40 PM
  3. Who's in charge?
    By chillin out in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-10-2006, 10:51 PM
  4. How do you charge a car A/C
    By dude in forum Air Conditioning
    Replies: 21
    Last Post: 02-04-2004, 09:36 AM
  5. Chillers versus packs
    By Peter_1 in forum Technical Speculations
    Replies: 15
    Last Post: 17-01-2004, 09:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •