Thread: weighing scales R-508b
19-07-2007, 11:17 AM #1
Hi all fridgemen can anyone help me, i need to find a set of weighing scales that are very accurate and that can hold back the high pressure of R-508b and R-23, because the gas charge has to be within the nearest gram with a minimal charge.
Kindest Regards
Graham.
19-07-2007, 02:14 PM #2
Re: weighing scales R-508b
Since you are into so small charge it is strange that your systems does not use a static charge. Much easier to handle and pretty exact +- if the all are
inside an ambient of 20c +- a couple of c. I use in a few cases else a fine needle valve on a tube from the bottles so the flow is so small so you can follow the grams slowly passing by and then close. You need those systems pretty dry so a filling weight can give you moisture by trapping under the low transfer temperatures.
Per
20-07-2007, 12:53 PM #3
I would suggest you use the scales for the correct charge and your well kept manifold as the shut off valve.
Have you looked at the ITE scale mod' WS-055 which has a resolution of 2 gr & accuracy of 1%.
20-07-2007, 01:14 PM #4
Sure a manifold should be involved, but they are for sure not good as a fine regulator and it is easy to get
50 bar's and up of pressure on the intake on the manifold so with bad luck you either "adjust" the pointers to a "new" range or overfill in a second. By using a fine needle valve or similar as a start point on the bottle side, you avoid a lot of surprises as I can see it. 95% at least of the many hundreds systems I filled over the Years have a static fill information which works well and give a more relaxed time doing it. Strange that this is not common in this case too.
22-07-2007, 04:17 AM #5
One of the field expiedeint regulators that I use is a lenght of cap tube brazed into a shreader on one end and brazed into a piece of 1/4inch and flared to go onto the tank.
Electronic weighing scales
By Lucas in forum Tools and CalculatorsReplies: 5Last Post: 30-09-2009, 10:34 AM -
Refrigerant charging weighing scale
By malik55 in forum Tools and CalculatorsReplies: 4Last Post: 06-11-2006, 11:14 PM -
Help, CPS scales, please help!
By sunwind in forum Technical DiscussionsReplies: 4Last Post: 05-12-2004, 10:31 AM