    low discharge tempeeature



    the compressor is twin screw type,Evaporationg Temperature=-3degC,Condensing temperature=43.5degC.But the discharge tempeeature is 48 degC! it should be more than degC,isn't it?



  2. #2
    Join Date
    Jul 2006
    Location
    Copenhagen
    Posts
    39
    Rep Power
    0

    Re: low discharge tempeeature

    What refrigerant?. I would say too much refrigerant on the system

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: low discharge tempeeature

    It sounds u u have refrigerant liquid slugging in ur screw compressor cools down the the discharge temperature to this degree. So it is better to check out the TXV bulb position or its size (perhaps it is oversized) or there is over charging in ur system. What is the sort of ur oil cooler system?.

    Regards

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: low discharge tempeeature

    The possibility of overcharging is more. Please also check the TEV wether it has been properly selected and if the same is operating.

  5. #5
    Join Date
    Apr 2007
    Location
    Phillipine
    Posts
    22
    Rep Power
    0

    Re: low discharge tempeeature

    Hi,
    Where is you location cause the equipment already size up to 43.5C and you have 48C discharge temp. also the refrigerant use, do include the oil. It is unusual to have that high temp. and still have high discharge temp. The factor is the impurity of both oil and refrigerant. The moisture inside the compressor and the system. Also the dirt on the condenser if it is aircooled clean it with water and if it shell and tube scrub it.

  6. #6
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: low discharge tempeeature

    Quote Originally Posted by mohamed khamis View Post
    It sounds u u have refrigerant liquid slugging in ur screw compressor cools down the the discharge temperature to this degree. So it is better to check out the TXV bulb position or its size (perhaps it is oversized) or there is over charging in ur system. What is the sort of ur oil cooler system?.

    Regards
    Wouldn't the compressor suction temp tell you this? Sticky frost on the suction line and no superheat at the compressor?

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. Screw discharge cooling
    By Volnei in forum Industrial Compressors
    Replies: 13
    Last Post: 05-11-2008, 09:24 AM
  3. Oil Leak in NH3 Discharge Line Flange
    By NH3LVR in forum Industrial
    Replies: 9
    Last Post: 26-05-2007, 09:15 PM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM
  5. Discharge Desuperheating Good or Bad?
    By Calvin Becker in forum Technical Discussions
    Replies: 10
    Last Post: 31-05-2003, 11:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •