    short of gas symtoms?



    hi, just running this by you guys<, an engineer i work with was telling me that icing back to the compressor are signs of lack of refrigerant on an r22 split wit a setpoint of 18, was i right in disagreing with him by saying that if there was a lack of refrigerant you would be getting abnormal tempartures after expansion and posssibly get ice on parts of the heat exchanger and then in turn get high superheat! too me icing up too comp would indicate no airflow, dirty coils etc also i heard someone a mention a high latent heat load can cause this problem... can someone give me there opinions?

    cheers



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: short of gas symtoms?

    Start with your thoughts first.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: short of gas symtoms?

    was i right in disagreing with him
    Yep, you were.

    Everything you said is pretty much true.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: short of gas symtoms?

    Hi there,

    Here is the lack of refrigerant symptoms:

    1- Low LP
    2- Low HP
    3- High super-heat
    4- Low sub-cooling
    5- Bubbles in the sight glass

    Sub-cooling is the best indication.

    When suction line is frosted then this could be from :

    1- The suction gas temperature is below 0°C. Means the suction pressure is low, for whatever reason.
    2- Liquid flood back.

    Lack of refrigerant is very simple to diagnose.

    Cheers
    Even Einstein Asked Questions

  5. #5
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: short of gas symtoms?

    thanks for replys lads, any ideas about a high latent heat load? cant really get my head around it....from what take from it is if the there humidity to remove from the air it takes so much watts of cooling to change condition of air and struggles to take down temp, any ideas on how this would cause icing of suction?

    rgrds

  6. #6
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: short of gas symtoms?

    No....When the system is operated under high latent load compared with the sensible the moisture drain off is only increased and no possibilities for frost to be existent on the evaporator coil unless the system is much overdesigned and the evaporatung temperature is below zero and it is very scarce to occur.

    Regards

  7. #7
    Join Date
    Jul 2007
    Location
    Vancouver, Canada
    Age
    49
    Posts
    97
    Rep Power
    17

    Re: short of gas symtoms?

    high latent heat load is the amount of moisture the load contains. on container reefer cargo certain loads are brutal for this ie. herring roe and certain frozen fish. both are packaged in a brine solution which is a water and salt solution. herring roe is -10c and will consistantly ice up evap coils which blocks air flow hence ices up compressors etc... frozen fish -23c does the exact same thing. this product makes it difficult to reach setpoint sometimes defrosting every 45 mins to 1 hour to achieve any results. alot of nuisance service calls but otherwise easy money!!

Similar Threads

  1. Compressor short cycling....
    By sbessettejr in forum Trouble Shooting
    Replies: 10
    Last Post: 02-04-2007, 05:09 PM
  2. Short Cycling blues & low pressure control switch
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 14
    Last Post: 09-04-2006, 09:28 PM
  3. Aircon strategy for a school hall with short lease?
    By mamborambo in forum Air Conditioning
    Replies: 13
    Last Post: 25-02-2006, 08:47 AM
  4. Walk in Cooler (short cycling)
    By Brandon in forum Trouble Shooting
    Replies: 11
    Last Post: 05-05-2003, 11:43 AM
  5. The slow leak, the intermittant short...
    By Dan in forum The Trail of Tears
    Replies: 16
    Last Post: 14-07-2001, 03:16 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •