    air handling unit design



    How to go about designing an AHU??i have the following data with me
    inlet air conditions-
    WBT-29 deg C
    DBT -40 Deg C
    Fan capacity-1000m3/hr
    Oulet air conditions
    RH-60%
    air temp-25 deg C
    how to calculate the heat load on the unit?
    what amount of water condensation will take place?
    Kindly guide me !



  2. #2
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: air handling unit design

    Quote Originally Posted by ama_singh View Post
    How to go about designing an AHU??i have the following data with me
    inlet air conditions-
    WBT-29 deg C
    DBT -40 Deg C
    Fan capacity-1000m3/hr
    Oulet air conditions
    RH-60%
    air temp-25 deg C
    how to calculate the heat load on the unit?
    what amount of water condensation will take place?
    Kindly guide me !
    Hi ama_singh

    Welcome to this forum. firstly are you sure about this data and what is the application in which u use this AHU. I think from this data the intake air is all fresh and the outlet air conditions is the indoor air conditions not the exit. Anyhow if u r sure about this data the design is :

    first, The AHU will include cooling coil (Dx coil) and reheater :

    the cooling coil capacity = (1000/3600)*1.2*(94.6-49.8) = 15.0 kW

    The outlet cooling coil is of 18°C and 90% relative humidity
    the removal moisture = (1000/3600)*1.2*(21.1-12.5) = 2.867 grams

    The heater capacity is = (1000/3600)*1.2* (56.0-49.8) = 2.1 kW

    so u locate the inlet and outlet conditions on pschrometeric chart then to reasch from the inlet to outlet u need two procees "cooling and dehimdified then reheating" . so i think u will need a cooling coil with capcity of 15 kw to 18 kW with face area of 20 inch * 8 inch R134a at te = 7.4C. i wish it could help

    Cheers

  3. #3
    ama_singh's Avatar
    ama_singh Guest

    Re: air handling unit design

    actually we are to replace the catalyst in the reactor so to provide good air conditions in the reactor for the person to work inside it we will use the AHU.
    the air will enter from one manhole and exit from another manhole of the reactor.it won't be recirculated.So how do i go about finding the heat load on the refrigeration unit based on the conditions i told you earlier.

  4. #4
    Join Date
    Apr 2008
    Location
    india
    Age
    41
    Posts
    5
    Rep Power
    0

    Question air handling unit design

    hello !
    i m new in HVAC
    can anyone tell me the following.

    how to calculate heat load?
    or
    how to determine TR required for AHU?

    please mail me on e-mail deleted

    thankx
    Last edited by frank; 28-04-2008 at 10:51 PM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: air handling unit design

    Make same research and then came here again with concrete questions:
    http://www.natresnet.org/conference/...ons/Storer.pdf
    http://tinyurl.com/4kmhxh
    Last edited by nike123; 27-04-2008 at 08:46 PM.

  6. #6
    ashish's Avatar
    ashish Guest

    Re: air handling unit design

    Hello,

    Deatails of AHU are as below :
    Model NO. :- CCTU-040
    Drawing No. :- 6070-1
    Sr.No. :- 006040657
    CFM/CMH :-3235/5500
    Fan Size :- RDH-315R Qty :-02 Nos
    Motor Kw/HP/P :- 3.7/5/2
    Motor Pulley :-139X2A
    Fan Pulley :- 140X2A
    Condition required is : 25 deg 45% RH
    Pl note :-Size of the room is 5.6X12.6X3 mtr.
    We keep tomato paste at 80-85 deg inside the room and allow it to cool to 30-35 deg cel.
    Pl suggest the solution as in winter we are not facing the problem but in summer it becomes an issue.


    Ashish Khare



    Quote Originally Posted by mohamed khamis View Post
    Hi ama_singh

    Welcome to this forum. firstly are you sure about this data and what is the application in which u use this AHU. I think from this data the intake air is all fresh and the outlet air conditions is the indoor air conditions not the exit. Anyhow if u r sure about this data the design is :

    first, The AHU will include cooling coil (Dx coil) and reheater :

    the cooling coil capacity = (1000/3600)*1.2*(94.6-49.8) = 15.0 kW

    The outlet cooling coil is of 18°C and 90% relative humidity
    the removal moisture = (1000/3600)*1.2*(21.1-12.5) = 2.867 grams

    The heater capacity is = (1000/3600)*1.2* (56.0-49.8) = 2.1 kW

    so u locate the inlet and outlet conditions on pschrometeric chart then to reasch from the inlet to outlet u need two procees "cooling and dehimdified then reheating" . so i think u will need a cooling coil with capcity of 15 kw to 18 kW with face area of 20 inch * 8 inch R134a at te = 7.4C. i wish it could help

    Cheers

  7. #7
    ednalds's Avatar
    ednalds Guest

    Re: air handling unit design

    Quote Originally Posted by mohamed khamis View Post
    Hi ama_singh

    Welcome to this forum. firstly are you sure about this data and what is the application in which u use this AHU. I think from this data the intake air is all fresh and the outlet air conditions is the indoor air conditions not the exit. Anyhow if u r sure about this data the design is :

    first, The AHU will include cooling coil (Dx coil) and reheater :

    the cooling coil capacity = (1000/3600)*1.2*(94.6-49.8) = 15.0 kW

    The outlet cooling coil is of 18°C and 90% relative humidity
    the removal moisture = (1000/3600)*1.2*(21.1-12.5) = 2.867 grams

    The heater capacity is = (1000/3600)*1.2* (56.0-49.8) = 2.1 kW

    so u locate the inlet and outlet conditions on pschrometeric chart then to reasch from the inlet to outlet u need two procees "cooling and dehimdified then reheating" . so i think u will need a cooling coil with capcity of 15 kw to 18 kW with face area of 20 inch * 8 inch R134a at te = 7.4C. i wish it could help

    Cheers
    can you please share the reference of your formula?
    Also, AHU does not include Dx coils. AHU cooling medium is usually chilled water and the Dx coil is for PU or Package unit.

    ______
    bad

  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: air handling unit design

    Hi there,

    For AHU or any equipment dealing with air you need to know pychrometric calculations. I suggest that you talk to an experience consultant otherwise learn pychrometric first.
    There are lots of issues involved to explain here.
    Even Einstein Asked Questions

  9. #9
    Polau's Avatar
    Polau Guest

    Thumbs down Re: air handling unit design

    Can someone tell me what is a supply and return means on a reefer panel?
    I have a reefer which shows an al22 which is "evaporator safety"
    The other problem the signal light for supply is off but the signal light for return is on. Tell me what I should do.

  10. #10
    panginies's Avatar
    panginies Guest

    Re: air handling unit design

    hi to all,im new here
    let me know abt sabroe screw comp running parameter settings

  11. #11
    bangnhan87's Avatar
    bangnhan87 Guest

    Re: air handling unit design

    hi all, I'm a new member.
    I'm designing an AHU with capacity'AHU:
    cooling coil: 358kW at condition:
    Inler air: DBT: 27 Deg C; RH:60%
    Fan capacity-35000m3/hr. Pressure: 350Pa
    outler air: DBT: 9 Deg C; RH:97%
    Fan capacity-35000m3/hr. Pressure: 350Pa.


    heat Load of room is 350kW, caculated by Trace700.


    It has a proplem. that's AHU'dimension is small. about 2.5Dx2.1Wx3H. so, i put the return air at position 2.1Wx3H. and that so,the fan'space is not enough only remain 1.4m while the fan's dimension is 1300mm , the distance from the fan to the cooling coil would be 100mm. I just wonder if it changes the wind flow going into the fan.
    what do you think about problem?

  12. #12
    Join Date
    Dec 2010
    Location
    Australia
    Age
    58
    Posts
    8
    Rep Power
    0

    Re: air handling unit design

    Hi there ok is it for your house or a commercial office ?
    Yes the correct way is to gather all the info but you know what? There is an easier way but I need the total floor area and total windows and also is the premises in a real hot or cold part of your country.
    Get this info and I'll give you a rock solid size system.

    Cheers
    Ps the amount of condensate is irrelevant as this will depend on the humidity of the day and how much of it is inside

  13. #13
    Vemuri.Murli's Avatar
    Vemuri.Murli Guest

    Re: air handling unit design

    Hi Sir,
    Can you Please give the formulas used in finding the coil capacity?I am having the formulae Ma*(h1-h2)*60/14000 TR which is not matching with you.i am new to HVAC,i just want to correct my self


    Quote Originally Posted by mohamed khamis View Post
    Hi ama_singh

    Welcome to this forum. firstly are you sure about this data and what is the application in which u use this AHU. I think from this data the intake air is all fresh and the outlet air conditions is the indoor air conditions not the exit. Anyhow if u r sure about this data the design is :

    first, The AHU will include cooling coil (Dx coil) and reheater :

    the cooling coil capacity = (1000/3600)*1.2*(94.6-49.8) = 15.0 kW

    The outlet cooling coil is of 18°C and 90% relative humidity
    the removal moisture = (1000/3600)*1.2*(21.1-12.5) = 2.867 grams

    The heater capacity is = (1000/3600)*1.2* (56.0-49.8) = 2.1 kW

    so u locate the inlet and outlet conditions on pschrometeric chart then to reasch from the inlet to outlet u need two procees "cooling and dehimdified then reheating" . so i think u will need a cooling coil with capcity of 15 kw to 18 kW with face area of 20 inch * 8 inch R134a at te = 7.4C. i wish it could help

    Cheers

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. Off-line Mitsi VRF leaks!
    By sinewave in forum Air Conditioning
    Replies: 8
    Last Post: 05-06-2007, 11:18 PM
  3. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM
  4. air handling unit
    By Lc_shi in forum Technical Speculations
    Replies: 5
    Last Post: 16-12-2004, 06:08 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •