    Prssure drop in discharge line.



    Measure in a carrier 30hk chiller, 2 circuits, each with a 40HP 06E compressor, R22, water cooled condenser.
    The high pressure gauge is connected to compresssor head, and it is 1 bar( about 15PSI) higher than measuring from condensor(16bar vs. 15 bar) .
    I remember design book said that pressure drop in discharge line is expected not excess 2 F saturated temp lost. but 1 bar drop is about 5F lost

    Is it a design bug?



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Pressure Drop

    Hi, Lin
    if your conenser pressure is at condenser outlet it is about right, but if the second higher pressure is being measured at the condenser inlet the pressure drop is too high.
    A high pressure drop in the discharge line may be a design error, or more likly your are now evaporating higher causing an increased mass and volume flow around the refrigeration system. Is the plant being used for the purpose it was designed for?
    Regards Andy.

  3. #3
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Lin, pls provide the discharge line OD and equivalent length. This information will help determine if the discharge line is undersized.
    Prof Sporlan

  4. #4
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    Andy,
    The pressure is measured on the top of condenser vessel. the evaporating pressure is 4.5Bar.
    Prof,
    there are a shutoff valve(Open completely of course), muffle, and about 1.5 meter pipe, i will get the OD later.

  5. #5
    brookbank's Avatar
    brookbank Guest
    I've come across discharge mufflers on chillers and also drilled plates fitted between service valve and compresssor (standard fitting) on Carrier compressor/ receiver sets.
    i would try these for P.D. before ripping out your condensor pipes
    hope this is helpfull!

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Muffler

    Hi, Lin
    the muffler would cause a pressure drop due to the nature of it's design, along with the service valve this could be the region of what you are seeing.
    This unit is a package unit? Sometimes when the pipe runs are short a designer would cut corners, remember these units are made in mulitiples, if you use a smaller line size you are saving not just on pipe but on the line components, when taking this over a number of units built per year the savings can be considerable.
    If the pressure drop is not causing any problems in the system and your are happy to live with the slight ineffeciency I would leave it. On the other hand if a change of pipe is envisaged you will have to up the size of the muffler also (check sizing from a manufacturers chart), the pressure drop is a product of all the discharge line components not just the pipe size.
    Another possibility is that the muffler has be added and sized per line size. The pressure drop may have been fine on that size of pipe if a muffler had not been added.
    Regards. Andy

  7. #7
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    1.5 meters of discharge line isn't very long. The Prof would also be concerned about the muffler
    Prof Sporlan

  8. #8
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    Thank all u.
    2 circuits have same symptoms, so i think not muffler or sevice valve fail.
    I would rather believe designer's neglect. it's unwise for money reson to undersize pipe.

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Symptom implies a problem. The overriding question is whether the pressure drop is normal for the muffler.

  10. #10
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    The discharge pipe od is 1-5/8".
    capacity is 112kw with 30C cooling water in and 7C chilled water out.

  11. #11
    Join Date
    Jul 2001
    Location
    Fuzhou, China
    Age
    50
    Posts
    35
    Rep Power
    0
    from "Coolpack" calculated results, the pressure loss in pipe is only 0.16bar. So the muffler mayber a problem.

    How to get info. about muffler's structure?

Similar Threads

  1. pressure drop of pump return line ammonia
    By Moeller in forum Fundamentals
    Replies: 5
    Last Post: 04-09-2007, 05:21 AM
  2. trap in discharge line?
    By frozen ocean in forum Supermarket Refrigeration
    Replies: 4
    Last Post: 11-12-2005, 03:29 PM
  3. Measure suction line pressure drop with thermometer
    By Steve Wright in forum Fundamentals
    Replies: 7
    Last Post: 17-09-2005, 11:05 PM
  4. Exploded discharge line
    By Peter_1 in forum Industrial
    Replies: 1
    Last Post: 05-05-2004, 09:47 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •