    Pipe Sizings for pump



    Hey ,

    Im trying to determine how to size my piping arrangement between my pump (Minorflow 25-120) and my Liquid Condensor.

    The pump has about 18-20meters of head, and has a 1" discharge. However in the pump spec it says that the discharge piping needs to be sufficiently large as to limit the velocity to 2.5-3 m/s. I believe my flowrate is somewhere between 2-4liters/second.

    Between my pump and condensor location have about 4 elbows, and 2meters of piping.

    How do you go about sizing calcs??

    Any help appreciated
    Cheers
    Nick



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: Pipe Sizings for pump

    Hi

    This may help

    http://www.pressure-drop.com/

    Paula

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Pipe Sizings for pump

    Hi nickjh,

    Please refer to Carrier Handbook of HVAC System Design. There is a full chapter on water pipe line. It is a 115 MB book, which I am sorry I can not upload

    Other than water pipe line you will get a lot of other informations on design of a refrigeration plant.

  4. #4
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    38
    Rep Power
    0

    Re: Pipe Sizings for pump

    Yes, 1" is too small. The pressure drop is not significant, at around 8.5meters, as you have short pipe length but you have problem with the high velocity of 7m/s. You have erosion issues. 40NB sch40 would give you about 3m/s velocity and a pressure drop of 2m.

    What is the pressure drop across the condenser? If that is also low, at the rated flowrate, the pump may operate at runout condition and overloads the motor. Discharge control becomes necessary in this case.

    Here is a good downloadable pressure drop calculator.
    http://www.xs4all.nl/%7Ekostermw/dP/

    PS: I considered no elevation and the flowrate is 4l/s

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Pipe Sizings for pump

    Hello Ravi,

    I hope you have considered the 4 nos of Elbows and the vertical length.

  6. #6
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    38
    Rep Power
    0

    Re: Pipe Sizings for pump

    Yes, 4 elbows were considered. You can notice from my post script that I didn't consider any elevation as it was not mentioned.

Similar Threads

  1. extra length v pipe size v additional charge
    By misterfixit in forum Air Conditioning
    Replies: 18
    Last Post: 03-01-2007, 07:57 PM
  2. pipe sizeing tool
    By Latte in forum Tools and Calculators
    Replies: 5
    Last Post: 10-12-2003, 11:32 PM
  3. Replies: 17
    Last Post: 25-08-2003, 09:56 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •