    Liquid entering into reci.compressor



    Dear all,

    I am regulerly having this problem while designing double stage reci.compressor pakage with interstage cooling fecility liquid ammonia entering into compressor and causing sever damages even though we are proviging electronic level switch for measuring liquid level & baffle plates in interstage vessel.

    Please any body give some usefull information.



  2. #2
    Join Date
    Mar 2006
    Location
    dallas, texas
    Age
    75
    Posts
    108
    Rep Power
    19

    Re: Liquid entering into reci.compressor

    The interstage cooler size is probably to small. You are causing higher velocity thru the tank then the size of the cross sectional area of the tank can allow both gravity, and dwell time to seperate the liquid from the gas stream.
    Lower the liquid level , add a mist eliminator, use a tortuorous path for the gas to suction. Do you have the booster disc submurged in the liquid? Try injecting the make up liquid into the disc line from the booster to the interstage cooler.

    just a few ideas i have used on this application.
    Bruce

  3. #3
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Liquid entering into reci.compressor

    Hi there,

    I am not an ammonia expert but as far as I know you have to have three level controls.
    one for low level which stops the liquid pump. Second one on the middle which energizes the solenoid valve to fill the separator. Third one on the high level which cuts off the compressor.

    I suggest that you find the reason why the separator is completely filled up.

    I am sure that ammonia experts will give you the best solution here.

    Cheers
    Even Einstein Asked Questions

  4. #4
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Liquid entering into reci.compressor

    I am not an expert in Ammonia system and as such am unable to suggest any thing. I am sure you will get the correct solution to your problem from the experts in this forum.

    Sorry for not being able to help you. I am learning about ammonia from this forum.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Liquid entering into reci.compressor

    Is the liquid entering the low-stage cylinders or the hi-stage cylinders?
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    44
    Posts
    8
    Rep Power
    0

    Re: Liquid entering into reci.compressor

    Thank's

    I have checked all operating level,high level & low ) level switch and solenoid valves are working well.


    Quote Originally Posted by lana View Post
    Hi there,

    I am not an ammonia expert but as far as I know you have to have three level controls.
    one for low level which stops the liquid pump. Second one on the middle which energizes the solenoid valve to fill the separator. Third one on the high level which cuts off the compressor.

    I suggest that you find the reason why the separator is completely filled up.

    I am sure that ammonia experts will give you the best solution here.

    Cheers

  7. #7
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    44
    Posts
    8
    Rep Power
    0

    Re: Liquid entering into reci.compressor

    it was high stage cyl's.


    Quote Originally Posted by US Iceman View Post
    Is the liquid entering the low-stage cylinders or the hi-stage cylinders?

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Liquid entering into reci.compressor

    Does your compressor have an intercooler mounted on the compressor package, or, a separate vessel for intercooling?

    If you are getting liquid in the hi-stage cylinders it is probably coming from the intercooler.

    Sometimes the intercoolers have TXV's to control the superheat into the hi-stage cylinders. If you are getting liquid there I would look into the TXV operation to start with.
    If all else fails, ask for help.


  9. #9
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Liquid entering into reci.compressor

    You need to post a sketch of the intercooler so we can se the design. They is a lot of science and some art that goes into the design.

    You can use Stokes Equation to calculate the max velocity which is determined by the density of the liquid, the vapor, surface tension of the liquid and vertical separation height.

    ASHRAE has a section on accumulator design which may help you.

    Ken

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Luiquid line vibration and liquid hammer
    By Infinity in forum Trouble Shooting
    Replies: 12
    Last Post: 09-02-2007, 10:22 PM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •