    Question re: Cooling Sea Water



    I need to maintain 400 liters of salt water at 6°C in a closed system. Outside air temperature at peak cooling periods averages between 18 and 22°C, but can be as warm as 30°C. The tank is 12mm molded plexiglass. Commercial cooling units rated for sea water available here range in power output from 350 to 4000 watts. How much power do I need? (Circulation pump achieves a throughput of approx 350L/Hour, if that is indeed relevant).

    Thanks for your help.



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Question re: Cooling Sea Water

    I would gues anywhere between 8 and 70kW. would also depend what else is in the tank.

    Most of our machines (trane) will also work with salt water and a capacity up to 1MW.

    We just installed two CGAN's on a fishtank for a zoo in Holland!

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Question re: Cooling Sea Water

    Welcome Gastronorm, we don't have enough figures to help you.
    Therefore, I agree Sanderh somewhere between 5 and 70 kW.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Question re: Cooling Sea Water

    You need the total volume of the tank and a time period that it has to be cooled in.

    Then you the total heat contained in the tank based on the delta T from 30 dC to 6 dC. This will give you the heat in the tank. total heat / time period = refig capacity.

    You also need to consider the method that the tank gets to the temp. is this a one tie pull down or is it a batch process or is there a cyclic load being dumped in the tank.

    Lots of questions, not many answers.

  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Question re: Cooling Sea Water

    Sounds like this is a display tank for fish and such, so living load.

  6. #6
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    Quote Originally Posted by Gastronom View Post
    I need to maintain 400 liters of salt water at 6°C in a closed system. Outside air temperature at peak cooling periods averages between 18 and 22°C, but can be as warm as 30°C. The tank is 12mm molded plexiglass. Commercial cooling units rated for sea water available here range in power output from 350 to 4000 watts. How much power do I need? (Circulation pump achieves a throughput of approx 350L/Hour, if that is indeed relevant).

    Thanks for your help.
    Hi Gastronom

    Firstly the cooling load of the chilling sea water is :

    = (350/3600)*4.2*(30-6) = 9.8 kW, u should add 15% over to compensate the heat gain from the surrounding to the tank therefore,

    the cooling capacity = 9.8*1.15 = 11.27 kW = 12 kW

    Thus u need almost a cooling unit with capacity of 12 kW to 15 kW.

    Regarding to the available unit is of 4.0 kW, u have to use a pump of capacity of 140.0 L/hour not 350 L/hour.

    Best regards

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    I remember that I had visited a client who wanted to make ice from sea water. They had three tanks with sea water and was being maintained at a temperature of about 4 Deg. C. These tanks were being used to store crabs. After which they were shipped out alive. The refrigeration plant was about 65 Kw. But the tanks were large.

    Compared to that, I feel load calculated by Mohamed Khamis is correct.

  8. #8
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    38
    Rep Power
    0

    Re: Question re: Cooling Sea Water

    Designing a system based upon the pull down loads brings unnecessary redundancy in cases related to process cooling.

    Suppose, if I consider 2hrs pull down time then the system capacity reduces by half to that calculated by Mohamed Khamis. Though the formula is correct, I would agree with other posters about lack of data.

  9. #9
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    Quote Originally Posted by Ravi View Post
    Designing a system based upon the pull down loads brings unnecessary redundancy in cases related to process cooling.

    Suppose, if I consider 2hrs pull down time then the system capacity reduces by half to that calculated by Mohamed Khamis. Though the formula is correct, I would agree with other posters about lack of data.
    Hi Ravi

    Unfortunately there is a big mixing between a continuous, tubular water chilling and intermittent stored water chilling . when u chill water from let us say 30°C to 6°C by continuous flow rate of 400 L/hr the cooling load calculation is totally different when u chill the same conditions of 400 L stored in a tank at a rest. In other term, if 400 L of water enter steadily a tank of 30C and exit of 6C each hour differs from 400 L of water was if 30C and u want to chill it to 6C with a pull down time of 2 or 3 hours. In the first case the cooling load is = 400/3600*4.2*(30-6) = 11.2 kW while in the second case the product load is = 400/(2*3600)*4.2*(30-6) = 5.6 kW. And this explain to u the difference in cooling load calculation in case of AC and Refrigeration applications which is Why in AC the product load is not involved in the cooling load calculations. I wish it is clear
    Cheers

  10. #10
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Question re: Cooling Sea Water

    So what is the 3600? Is this a constanant for salt water?

    What is the constanant for fresh water?

    All so where does the 4.2 come from?

    I'd enjoy learning more about this formula and how to apply it, so far this thread has been interesting.

    Thank you.
    Last edited by The MG Pony; 12-07-2007 at 05:14 PM.

  11. #11
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Question re: Cooling Sea Water

    3600 is 60*60, the number of seconds in an hour.

    4,2 kJ/kg*K is specific heat for water

    Q=m*c*dT

    Q= heat in kJ/s (kW)
    m= mass or mass flow (kg or kg/s)
    c= specific heat in kJ/kg*K
    dT= temperature difference.

  12. #12
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Question re: Cooling Sea Water

    Ah Ok, cool, thanks!

    Now I tried using the formula a fiew times, Now my aplication is much the same, how ever I know the exact heat in, and the volume of the water that it is going into

    400 Watts/H In total (Some times less)
    2 L Total system volume
    1100L/H
    This is for chilling water for cooling a computer system @ 0C to -30C Or for times I want to to figure out how to cool say 64L of water down from say 25C to 4C in 4-5 Hours (For cooling drinks in an average camping cooler) what formula do I use for thees cases? as when I use the above I get massive numbers that are much to big for the intended aplication.

    Do I simply take the resualting number and devide it by the number of hours it can take?
    Last edited by The MG Pony; 12-07-2007 at 08:03 PM.

  13. #13
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Question re: Cooling Sea Water

    Yep! But then the time in seconds, not hours!

  14. #14
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    Quote Originally Posted by The MG Pony View Post
    So what is the 3600? Is this a constanant for salt water?

    What is the constanant for fresh water?

    All so where does the 4.2 come from?

    I'd enjoy learning more about this formula and how to apply it, so far this thread has been interesting.

    Thank you.
    Hi The MG Pony

    3600 = is the conversion factor from L/hr to L/s

    constant for water is named here specific heat 9kJ/(kg.K) and it equals to 4.187 at 25C but for salted water it is slightly larger than that due to the salts concentration and yet i don not have this value and i took it as 4.2 kJ/(kg.K) so i mentioned in the first post here in the froum the cooling load swings between to 12 kW and 15 kw to take into account any diversity factor. and thank u for ur courtesy. I'd like to be in ur service

    cheers

  15. #15
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    Quote Originally Posted by The MG Pony View Post
    Ah Ok, cool, thanks!

    Now I tried using the formula a fiew times, Now my aplication is much the same, how ever I know the exact heat in, and the volume of the water that it is going into

    400 Watts/H In total (Some times less)
    2 L Total system volume
    1100L/H
    This is for chilling water for cooling a computer system @ 0C to -30C Or for times I want to to figure out how to cool say 64L of water down from say 25C to 4C in 4-5 Hours (For cooling drinks in an average camping cooler) what formula do I use for thees cases? as when I use the above I get massive numbers that are much to big for the intended aplication.

    Do I simply take the resualting number and devide it by the number of hours it can take?
    for 64 L, the chilling time is 4 hours and factor of safty is of 15%

    cooling load = 64/(4*3600)*4.2*(25-4)*1.15 =0.5 kW

    therefore u need almost 0.5 kw to 1.5 kw as a system cooling capacity. however i think 4 hours as chilling time is big so what about a hour or two hours i think it reasonable. I wish it could help

    Cheers

  16. #16
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Question re: Cooling Sea Water

    Quote Originally Posted by The MG Pony View Post
    Ah Ok, cool, thanks!

    Now I tried using the formula a fiew times, Now my aplication is much the same, how ever I know the exact heat in, and the volume of the water that it is going into

    400 Watts/H In total (Some times less)
    2 L Total system volume
    1100L/H
    This is for chilling water for cooling a computer system @ 0C to -30C
    For this case i can not understand some figures as "400 Watts/H" what this "H" it refers to hours and i think no becuase this power not energy then this is very small cooling capcity. what 2 L and 1100 L/H which of both is the water capcity. What about 0C to -30C the water must frist enters at ambinet condition or less than that by 4 - 5 K not at 0C. Pls clarify that to give a light.

  17. #17
    Join Date
    Mar 2007
    Location
    India
    Age
    51
    Posts
    38
    Rep Power
    0

    Re: Question re: Cooling Sea Water

    For any coooling system, be it for HVAC or process, we have to consider the end load and this is our objective for deciding a cooling system. Once, the fluid is cooled to 6C from 30C, this 6C fluid is used to cool a process and then temperature rises depending upon the load, for a constant flowrate. Now mass flowrate times specific heat times the new temperature difference is the actual load experienced by the cooling system on a routine basis.

    Most of the heat transfer equipment, for cooling, use a temperature differece of 5C for economical heat transfer device sizing and that is why I posted those comments and not to point out anything against your post.

    That is why, I once again reiterate for more data from the OP.

  18. #18
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Question re: Cooling Sea Water

    I figured it out thanks.

    A computer puts in 400watts of energy so 400watts per houre.

    System volume is 2L and flow is 1100L per houre.

    Average opperating temp will be for the end user -30C.

  19. #19
    Join Date
    Feb 2007
    Location
    UK
    Age
    55
    Posts
    53
    Rep Power
    18

    Re: Question re: Cooling Sea Water

    Be aware of the specific heat of sea water.The salt makes it act like Brine solution which has a much lower specific heat than pure water, so you may need to revise the calc for the difference.

Similar Threads

  1. Cooling down the water in a 1000 liter container
    By Joep Hogenhout in forum Technical Discussions
    Replies: 29
    Last Post: 21-04-2009, 01:27 AM
  2. cooling water TDS
    By afeef in forum Technical Speculations
    Replies: 1
    Last Post: 19-04-2009, 07:38 AM
  3. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •