Thread: 12kw workin a 5kw load
-
02-07-2007, 03:02 AM #1
12kw workin a 5kw load
hi,i have a site that has a daikin vrv with multi box installation, conditioning an open plan office space...... 12 x 12 kw indoor heat exchangers serving the floor....the client that has moved on to this floor is looking to put 5 additional partioning up to make offices and meeting rooms...as its design is open plan temp problems may occur in new rooms...my question is there any problem in getting one of thes4e 12kw to look after one of these rooms that a 5 kw could handle...
cheers
-
02-07-2007, 09:33 PM #2
Re: 12kw workin a 5kw load
Hi Phil,
This is often a problem with these type of buildings.
The design consultants usually work to an open plan environment and specify VRV/VRF systems to suit the application. This is always more or less accepted until a few months down the line and a new tennant will take over occupancy and decide to make a 'couple' of alterations. This makes life a little bit harder!
You have a couple of options on this one.
option 1: Just keep the 12kw unit and use it in a smaller office.
option 2: Give the client a price to make ammendments to the system.
Your probably best to stick to option 1 because one day the office may revert back to open plan.
Jase
-
02-07-2007, 11:31 PM #3
Re: 12kw workin a 5kw load
hi jase, i agree with you there, just wasnt 100% if it would over shoot temp too much or get draughts etc...suppose pmv will look after the amount going to exchanger and keep her on low fan speed...its in the bag!
cheers
-
04-07-2007, 12:22 PM #4
Re: 12kw workin a 5kw load
hi phil,
what model outdoor and indoors do you have?Paul
"KEEP IT COOL"
Similar Threads
-
Heat Load Selection for EOT Cabin A/C in Steel Plants
By Samarjit Sen in forum Tools and CalculatorsReplies: 12Last Post: 19-11-2010, 12:17 PM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Cooling Load Calculation
By jervame_sireh in forum FundamentalsReplies: 0Last Post: 21-04-2007, 11:05 PM -
AKV versus higher load
By Peter_1 in forum IndustrialReplies: 20Last Post: 18-04-2004, 11:05 AM -
Load Calculation / Comaprison
By herefishy in forum Technical SpeculationsReplies: 11Last Post: 04-03-2002, 09:21 PM