    12kw workin a 5kw load



    hi,i have a site that has a daikin vrv with multi box installation, conditioning an open plan office space...... 12 x 12 kw indoor heat exchangers serving the floor....the client that has moved on to this floor is looking to put 5 additional partioning up to make offices and meeting rooms...as its design is open plan temp problems may occur in new rooms...my question is there any problem in getting one of thes4e 12kw to look after one of these rooms that a 5 kw could handle...

    cheers



  2. #2
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: 12kw workin a 5kw load

    Hi Phil,

    This is often a problem with these type of buildings.
    The design consultants usually work to an open plan environment and specify VRV/VRF systems to suit the application. This is always more or less accepted until a few months down the line and a new tennant will take over occupancy and decide to make a 'couple' of alterations. This makes life a little bit harder!
    You have a couple of options on this one.

    option 1: Just keep the 12kw unit and use it in a smaller office.

    option 2: Give the client a price to make ammendments to the system.

    Your probably best to stick to option 1 because one day the office may revert back to open plan.

    Jase

  3. #3
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: 12kw workin a 5kw load

    hi jase, i agree with you there, just wasnt 100% if it would over shoot temp too much or get draughts etc...suppose pmv will look after the amount going to exchanger and keep her on low fan speed...its in the bag!

    cheers

  4. #4
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    974
    Rep Power
    19

    Re: 12kw workin a 5kw load

    hi phil,

    what model outdoor and indoors do you have?
    Paul


    "KEEP IT COOL"

Similar Threads

  1. Heat Load Selection for EOT Cabin A/C in Steel Plants
    By Samarjit Sen in forum Tools and Calculators
    Replies: 12
    Last Post: 19-11-2010, 12:17 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. Cooling Load Calculation
    By jervame_sireh in forum Fundamentals
    Replies: 0
    Last Post: 21-04-2007, 11:05 PM
  4. AKV versus higher load
    By Peter_1 in forum Industrial
    Replies: 20
    Last Post: 18-04-2004, 11:05 AM
  5. Load Calculation / Comaprison
    By herefishy in forum Technical Speculations
    Replies: 11
    Last Post: 04-03-2002, 09:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •