    TEV after a defrost



    Is the TEV wide open after an electrical defrost in case of a pump down and in the case of not pumping down where pressure can build up while defrosting?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: TEV after a defrost

    Quote Originally Posted by Peter_1 View Post
    Is the TEV wide open after an electrical defrost in case of a pump down and in the case of not pumping down where pressure can build up while defrosting?

    Hi ya Peter.
    I would of thought that the valve would be wide open initialy straight after the defrost because of the increased superheat in the suction line.
    As regards the pump down or not, I would think that again the valve would be open due to the increased temp caused by the electric defrost.

    Cheers taz.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: TEV after a defrost

    Hi Peter

    I think the one on pumpdown would be more open than the one not on pumpdown, assuming the valves and evaporators reach the same temperature on defrost.

    Silly thought time, should we not call it defrost and refrost

    Jon

  4. #4
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: TEV after a defrost

    Quote Originally Posted by Peter_1 View Post
    Is the TEV wide open after an electrical defrost in case of a pump down and in the case of not pumping down where pressure can build up while defrosting?
    Hi Peter_1

    Of course, the TXV is wide open in the pumping down system comparing to that in not pumping down. The reason is in pumping system the mount of still refrigerant in the low-side is small as a result of the most of the refrigerant is entrapped behind the solenoid valve and settled in the receiver. Accordingly, when the electrical defrost is activated the degree of superheat is increased significantly with a small evaporating pressure (small refrigerant amount), the net resultant force applied on the TXV diaphragm is accounted for a favor of more opening area of the TXV port. And of course the two TXV are balanced port to cancel the effect of the pressure drop on the the TXV port.

    Cheers

Similar Threads

  1. Freezer Room Defrost
    By Samarjit Sen in forum Commissioning
    Replies: 23
    Last Post: 21-06-2007, 06:16 AM
  2. electromagnetic defrost heat pump?
    By star882 in forum New Technologies
    Replies: 8
    Last Post: 08-03-2007, 10:09 AM
  3. Hot Gas defrost suction pressure regulation
    By 87mustang in forum Technical Speculations
    Replies: 5
    Last Post: 05-08-2005, 07:25 AM
  4. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM
  5. Hot gas/Cool gas defrost
    By JONAH in forum Technical Discussions
    Replies: 9
    Last Post: 10-04-2002, 12:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •