Thread: Rack System
    May 2006
    India
    82
    1,013
    Rack System
    What is the oil management components and system for a Rack System. Can this system be applied for low temperature system where a number of rooms with varied temperatures are to be catered too.
    Oct 2006
    1,843
    21
    Re: Rack System
    Quote Originally Posted by Samarjit Sen View Post
    Oil management for rack or Pack as we call them in the UK are many and varried.
    But they have common features.
    The oil is removed from the discharged gas by a seperator and is then passed either directly to the comps or to a small oil receiver. This receiver is not normaly kept at discharge pressure, normaly the pressure is vented back to suction and the oil is kept at a few bar above suction pressure.. The oil is filtered and then goes back to the comps. It is let into the comp either by a float valve assembly or by a solenoid valve that is operated by sensors.
    The systems work for high temp, low temp or mixed temp systems, the only difference is the delivery pressure of the oil.
    There are many, many methods and every pack manufacturer uses thier own prefered system.
    They are prone to oil filters blocking and false readings on some electronic controlers but for the most part they are reliable and work well.
    Cheers taz.
    Aug 2005
    5,302
    Re: Rack System
    Samarjit,
    Here is a link to a useful article from Sporlan...
    http://www.sporlan.com/SD-129.pdf
    May 2006
    India
    82
    1,013
    Re: Rack System
    Thank you Taz24 and US Iceman,
    Temprite are also making something similar.
    Aug 2005
    5,302
    Re: Rack System
    Henry Technologies also owns the old AC&R product line too I believe for anyone interested in another potential source.
    http://www.henrytech.com/
    Here is a document on their system operation.
    http://www.henrytech.com/Tips/HT-TT6.pdf
    May 2006
    India
    82
    1,013
    Re: Rack System
    Thank you US Iceman
  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Fan model for system optimization
    By autt in forum System Optimization
    Last Post: 31-03-2007, 05:34 AM
  5. Refrigeration system proposal; comments please.
    Last Post: 01-01-2003, 03:42 PM