    Question Heatpump for water & Space heating?



    Dear RE Members.

    I am absolutely new to the in-depth workings of refrigeration systems. I understand the basic principles.and have some experience in the electrical control of HVAC systems.

    I am considering the possibility of using my Mitsubishi heatpump to heat (Pre-Heat) my domestic hot water.

    I have a 16KW (heating multisplit) unit
    Model MXZ-8A140VA
    REFRIGERANT R410A

    The cylinder I have has a stainless steel coil inside the tank.

    The coil has a surface area of 1,1M2(Square meter)
    Diameter of 20mm
    I think this has a KW Rating of more or less 32KW

    My Question is:
    If I were to turn all other circuits OFF and dedicate the total capacity (16KW) to this coil will it work as a water heater?

    What possible problems could I face

    Once I receive some answers/suggestions I will ask a few more questions.

    Thanks for your reply in advance.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Heatpump for water & Space heating?

    Do you all ready have a hydronic heating system? For a well made under floor hydronic system you only need water of 35C. At 35c constant flow of a 5c swing your heat pump will handle this no problem, as will most systems, I my self am making a 5Kw hydronic heating system via a coaxial exchanger (Plate will be much better for this how ever).

    For domestic hot water the max temp will be 40C, too low for health codes due to Legionnaires disease if I recall correctly, the system must reach 70C.

    If you go into the heat pump section you will find better info, take a look at my project too for some ideas along with some others there.

  3. #3
    Join Date
    Jan 2006
    Location
    romania
    Age
    59
    Posts
    6
    Rep Power
    0

    Re: Heatpump for water & Space heating?

    The heat pump utilisation is O.K. for low temperature hydronic systems (35 - 45 Celsius). That means underfloor heating and ventiloconvectors (fan coil units).
    If you want a higher temperature it`s possibile to opperate at 55 (max. 60) Celsius deg., but the COP will be lower.
    For DHW, i recomand you to use a tank with two coils. First for water preheating (up to 40-45 Celsius deg.) with heat pump and the second will be conected to a boiler to give 55-60 Deg. and also for antilegionella !

  4. #4
    Join Date
    Sep 2007
    Location
    Belgium
    Posts
    14
    Rep Power
    0

    Re: Heatpump for water & Space heating?

    Most heat pump manufacturers include domestic water heating, so it's perfectly feasible but COP will drop.
    For Legionnaires disease I think the system must be able to reach 70 °C but only temporarily. An electric resistance can be used...

Similar Threads

  1. Fuji AOY45 cassette Problem (no heating)
    By R B M 72 in forum Air Conditioning
    Replies: 8
    Last Post: 09-03-2011, 08:30 PM
  2. fresh air heating in cold area
    By Lc_shi in forum Air Conditioning
    Replies: 7
    Last Post: 14-05-2009, 01:37 AM
  3. Domestic Space and Water Heating
    By Rosy in forum Heat Pumps
    Replies: 13
    Last Post: 19-04-2007, 07:42 PM
  4. Heating problem
    By meadows in forum Trouble Shooting
    Replies: 7
    Last Post: 01-07-2006, 11:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •