    Freus, water cooled, change gas?



    I installed a Freus, with a built in cooling tower, on a workshop. The sump water is in the low seventies. The pressures are 175/70. It never condenses water out of the air. I want to change from R-22 to 404a or 410 & am willing to change the oil to POE. My theory is I'd get an evaporator cold enough to dehumidify the air & reduce the enthalpy. What is wrong with this idea?



  2. #2
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Freus, water cooled, change gas?

    Quote Originally Posted by Dennis Williams View Post
    I installed a Freus, with a built in cooling tower, on a workshop. The sump water is in the low seventies. The pressures are 175/70. It never condenses water out of the air. I want to change from R-22 to 404a or 410 & am willing to change the oil to POE. My theory is I'd get an evaporator cold enough to dehumidify the air & reduce the enthalpy. What is wrong with this idea?
    Hi Dennis Williams

    From ur data, the evaporating temperature is 0.2°C i.e. coil dew point temperature of almost of 3 to 6°C and condensing temperature of 30°C with R-22. It sounds the system is undercharging case or the evaporator blower is oversized and blows a high flow rate of air than required. Although u can find the coil surface temperature is very small but u did not find considerable condensate flow rate, the dehumidification process depends on the coil surface temperature plus the cooling capacity as well the entering air humidity. could u cite more data for help.

    cheers

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Freus, water cooled, change gas?

    For starters, you have way too much evaporator airflow. Kick the blower down a notch.

    Ideally, the blower speed should be adjusted so that at thermostat cutout the supply air temperature (measured close to the coil) is about 21F lower than the temperature at the thermostat.

    IOW, if the thermostat is set to cut out at 75F, the supply air temp should be about 54F when the system shuts off.

    The lower the airflow, the colder the supply air... and vice versa.

Similar Threads

  1. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  2. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  3. How to adjust head on a water cooled condenser
    By kengineering in forum Technical Speculations
    Replies: 5
    Last Post: 30-05-2007, 10:37 PM
  4. water cooled
    By tait71 in forum Trouble Shooting
    Replies: 27
    Last Post: 02-03-2007, 06:22 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •