    Heat Pump Modification



    i finished my first year NVQ 2 COLLEGE IS CLOSE NOW WE HAVE BEEN THOUGH THAT CONDENSERS ARE BIGGER THAT EVAPORATOR IF IT IS THE CASE.

    1/ WHAT IS THE PHENOMENON OF HEAT PUMP SYSTEMS WHERE BOTH COILS ARE EQUALE?

    2/ASSUME I MODIFY THE HEAT PUMP BY ADDING A AN EVAPORATOR BOX AND LIQUID RECEIVER WILL IT WORK AS HEAT PUMP AND COOL ROOM?

    PS: ALL CALCULATION MUST BE TAKEN IN CONSIDERATION.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Heat Pump Modification

    Hi, no need to SHOUT

    1) Who says that they are the same size ?

    2) Don't understand the question, heat pumps will normally work in both directions as standard.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Arrow Re: Heat Pump Modification

    Evaporator extracts heat at a DT of 6 to 10 K and the condensors rejects this heat and the absorbed compressor power back with a DT of 15K back to the outside.
    So the 15K is at least twice or 1.5 bigger then the 6K, so the condensor can be half the size of the evaporator .
    Most condensors have a fin spacing half of that of the evaporator, so again a reason why the condensor is smaller.
    And your instructors told you that condensors in general are bigger????
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. Will this heat pump work?
    By goodguy in forum Heat Pumps
    Replies: 7
    Last Post: 08-03-2008, 04:14 PM
  4. Rebuild air2air heat pump
    By stalker in forum Technical Speculations
    Replies: 3
    Last Post: 02-11-2006, 10:10 AM
  5. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 07:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •