    Differce of 50 hz and 60hz



    Hai engineers,
    How is the after effect if 50 hz compressor work in the 60 hz 220 v suplay, also 60 hz in 50 hz suplay . Thanks.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Differce of 50 hz and 60hz

    there is 10Hz difference!

    Or rather the 50Hz compressor will run faster on the 60Hz the inverse is true as well; A 60Hz compressor will run slower on a 50Hz supply and capacity will fluctuate along with rotational speed.

  3. #3
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Differce of 50 hz and 60hz

    Hi First of all Compressor manufacturers make dual voltage Compressors thus they can be run on 50 or 60 Hz depending which area the instalation is.

    Toosh

  4. #4
    Join Date
    Jun 2007
    Location
    Norway
    Age
    74
    Posts
    56
    Rep Power
    17

    Re: Differce of 50 hz and 60hz

    Quote Originally Posted by jaison View Post
    Hai engineers,
    How is the after effect if 50 hz compressor work in the 60 hz 220 v suplay, also 60 hz in 50 hz suplay . Thanks.
    I am working a lot with 60hz compressors from USA
    here in Norway and find that the maximum voltage often is rated lower on 50hz. The compressors takes more amps due to the lower speed. The Copelands I use in cascade systems are rated 208-230v 60hz and only 200-220v at 50hz.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Differce of 50 hz and 60hz

    We had a real bad time with the solid state cam timers on some Y**k air cooled condensers some years back.

    Apparently, the units were made in the USA then shipped over to France where they were rewired to comply with local regulations.

    It transpired that the timers were rated for 60hz and couldn't operate properly on the UK electric supply??

    Well, thats what Y**k said.

    P.S.

    Haven't touched ANY Y**k kit since - back up was less than helpful.

    I've got some photo's somewhere of the wiring, I'll dig them out and post them - should cheer you up

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Differce of 50 hz and 60hz

    Attached Photo

    Note the old ICI R22 cylinders
    Attached Images Attached Images

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Differce of 50 hz and 60hz


    As the service manager said, "Just do a bit of fault finding, the Y**k manual and drawings should be on site."

    Yeah, right.

    Just follow the white wire from the hidden sensor
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Mar 2007
    Location
    uae
    Age
    44
    Posts
    24
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    Have any way to run 60 hz compressor on 50 hz suplay at normal amps.

  9. #9
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Differce of 50 hz and 60hz

    Hi Jaison,
    60 Hz motor will run on 50 Hz but at reduced speed. The synchronous speed of 60 Hz is 7200/no. of Poles and for 50 Hz is 6000/no. of poles....thus 2 pole motors run at 3600 rpm (less slip) on 60 Hz and 3000 (less slip) rpm on 50 Hz.
    Expect about 17% reduction in refrigeration capacity.
    As to current draw (and motor protection devices) and compressor motor thermal state you will need to address these issues separately.
    Are these compressors single or 3 phase? If 3 phase and capacity and current draw are critical then think about supplying compressors from an Variable Speed Drive.....ths will get round your problem.

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Differce of 50 hz and 60hz

    All refrigeration manufacturers and other equipment suppliers have both the 60 Hz and 50 Hz and also the different volts. While ordering you have to select as electricity conditions and select the same . In our country we have 50 Hz, 3 pahes 380/400 volts AC supply. We are getting the compressors and the Evaporators from USA and Europe for this application. A 60 Hz being operated at 50 Hz will reduce the speed and the reverse will increase the speed.

  11. #11
    Join Date
    Jun 2007
    Location
    Sri Lanka
    Posts
    88
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    All compressor & other electrical manufacturers through out the world manufacture electrical appliances for the electrical supply prevailing in that particular country. Therefore when you order you must specifically state the electrical supply of your country. So they will supply with the correct voltage & cycle. If you use 60 Hz with a supply of 50 Hz, the performance of the compressor will be less and due to less in voltage. It will get heated up than the normal level. During summer in UAE some times the compressor will trip off due to overheating.

    Viz, same will apply if you use 50 Hz with a supply of 60 Hz. It will give increase performance due to higher speed and the winding will get heated up. The winding coils will burn after some time. You can not operate for a reasonable period of time. Further please bear in mind that compressors are manufactured to generate certain amount of heat during gas compression. Therefore the extra heating of the compressor is injurious to it. To overcome this problem you could install a electronic speed driver which will give necessary voltage & the cycle for the equipment but this is more expensive than the compressor. So you have to decide to throw or use it….

  12. #12
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Differce of 50 hz and 60hz

    Don't throw em out! Throw em on ebay and recover your investment!

  13. #13
    Join Date
    Mar 2007
    Location
    uae
    Age
    44
    Posts
    24
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    Hai Electrocoolman,
    I am asking about the 220v 50hz , but compressor working in 60 hz, so running ammps became high. I wants to reduce the amps, any capacitor can reduce the amper?. Thanks for your detailed reply, also please think for me about this note. THANKS

  14. #14
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Differce of 50 hz and 60hz

    Hi Jaison,
    Sorry for not replying sooner but have been busy working....
    So as I understand, you have a 220v 50Hz compressor which you want to run on 60Hz, but when you do, it draws too much current.?

    What is the line voltage of your supply?
    What is the make and model of the compressor?
    What is the actual plate details on the compressor...i.e. is there a voltage range on the plate?

    The 50Hz compressor will run faster on 60Hz, thus the system refrigeration capacity will be increased. If the system is a precharged capillary system it could be that the system is overloaded as it will be pumping more refrigerant and thus you might be 'overcharged'.
    Have you checked the system pressures? Too low suction and too high on head pressure / condenser only partially available due to excess refrigerant, causing your high compressor current.?

    Just a thought....but await further info.
    Adrian.

  15. #15
    Chillerguy's Avatar
    Chillerguy Guest

    Re: Differce of 50 hz and 60hz

    We have come across this several times. You want to run the 60hz voltage but at 50 hz, correct? The only way we have been able to overcome it is to use a transformer to buck down the voltage to the 50hz rating. Otherwise you will draw to much current and burn up the motor.

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Differce of 50 hz and 60hz

    Quote Originally Posted by Chillerguy View Post
    We have come across this several times. You want to run the 60hz voltage but at 50 hz, correct? The only way we have been able to overcome it is to use a transformer to buck down the voltage to the 50hz rating. Otherwise you will draw to much current and burn up the motor.
    Using a transformer will certainly reduce/increase the voltage but the frequency will stay the same.

    To alter the frequency you need an electronic frequency converter

  17. #17
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Differce of 50 hz and 60hz

    Hi Jaison

    Have you cured your problem yet? We're all waiting....

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Differce of 50 hz and 60hz

    Quote Originally Posted by Electrocoolman View Post
    The 50Hz compressor will run faster on 60Hz, thus the system refrigeration capacity will be increased. If the system is a precharged capillary system it could be that the system is overloaded as it will be pumping more refrigerant and thus you might be 'overcharged'.
    .
    If it runs faster like you said, then for a given evaporator it will evaporate lower and evaporating lower is drawing less running current. Agree?
    The system will balance to a new point but this isn't that easy to calculate or predict.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Jun 2007
    Location
    Ruba 'el Khali
    Age
    39
    Posts
    30
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    The company my dad works for installed several British made splits units during 80 and early 90's. I forgot the brand name but their indoor unit was quite class and build quality was fantastic. Their compressors were all rated for 50Hz as indicated by their spec plate and been running fine on 60Hz supply in Saudi Arabia. My unit is still functional since purchased new in 80's. Nobody ever faced a complain, incident or damage due to difference of frequency.

    There wasn't a 60Hz version from OEM. When my dads employer decided to import them in Saudi, they tested a few units found them working fine and proceeded with bulk imports.
    Last edited by theboss; 12-07-2007 at 01:10 AM.

  20. #20
    Join Date
    Aug 2007
    Location
    Malawi
    Age
    41
    Posts
    19
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    Quote Originally Posted by jaison View Post
    Hai engineers,
    How is the after effect if 50 hz compressor work in the 60 hz 220 v suplay, also 60 hz in 50 hz suplay . Thanks.
    Does the name plate indicate both frequencies?

  21. #21
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Differce of 50 hz and 60hz

    The main issue is the motor. The compressor itself can easily be operated at the rpm coresponding with the suplied Hz.

    This is how it works:
    A motor designed for 220V 50Hz draws some amps and output some power. At 60 Hz the rpm is increased with 20% and the power output also increases with 20% when driving a compressor at the same operating pressures. In order to acheive 20% increase in power output either the voltage or amps have to increase.
    The copper wire in the windings in the motor is designed for a maximum amps rate. This amps is stated on the name plate. If this amps is exceeded the windings develop to much heat and the motor can overheat and burn.

    When this 50 Hz motor is operated on a 60Hz 220V grid the amps will increase with aproximately 20% and possibly exceed the max amps on the nameplate. If on the other hand the voltage was increased with 20% the amps wouldnt change at all and all would be fine. A 50Hz 220V motor will operate fine on a 60Hz 264V grid!

    The heat developed in the motor will increase with aproximately 20% but this shouldnt be to much of a problem for a compressor if the running conditions is resonable.


    On the other hand a motor designed for 230V 60Hz but running on a 50 Hz grid should have the voltage decreased with 17%. (50 is 17% of 60)
    The corect voltage for a 230V 60Hz motor running on a 50Hz grid is 192v!

    If this was the done the amps would be the same as on 60Hz and the power output would be decreased with 17% du to the redused speed. The heat developed in the motor would also decrease with aproximately 17%. And the motor would be quite happy.

    On the other hand if the voltage wasnt decreased, lets say still 230V on the 50Hz grid this would cause an considerable increase in the amps even in face of the 17% decrease in power output! As in the first example this could easily led to the amps exceeding the max allowed as stated on the nameplate.

    This is a very simplified explanation on the relationship between the voltage and the Hz on AC 3 phase motors. But it should still give the most important informations on the subject.

  22. #22
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Differce of 50 hz and 60hz

    I see a lot of 60Hz equipment that gets another reduced rating set for running at 50 Hz. Never seen it the other way around.
    Take the V out of HVAC and you are left with a HAC job

  23. #23
    kahootshop's Avatar
    kahootshop Guest

    Re: Differce of 50 hz and 60hz

    Hi ,
    I am thinking of importing a used carpigiani batch freezer abd also other refregration stuff from US, as it is very expensive in UK. The apparent problem is is famous 60hz v/s 50hz in uk. Do I need to do major changes with the machine like 50hz compressor change etc or there is some other solution. Can you recommend any refgiration engineer who can do this kind of job. I am in Croydon,london, UK.Please send your reply to my personal email address as well
    zammurad@gmail.com

    the specs of Carpigiani ice cream bath freezer are
    Electrical Requirements
    Voltage
    Phase
    Cycle
    Breaker Size
    208-230 1/3 60 Hz 50 Amps/40
    Running Amps: 39/31 Number of Feeders: 1
    kind regards and many thanks

  24. #24
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: Differce of 50 hz and 60hz

    Quote Originally Posted by frank View Post
    We had a real bad time with the solid state cam timers on some Y**k air cooled condensers some years back.

    Apparently, the units were made in the USA then shipped over to France where they were rewired to comply with local regulations.

    It transpired that the timers were rated for 60hz and couldn't operate properly on the UK electric supply??

    Well, thats what Y**k said.

    P.S.

    Haven't touched ANY Y**k kit since - back up was less than helpful.
    I tried to buy one of those cam timers , they wanted almost $1000 for it and they are almost identical to the washtech/starline or older comender comercial dishwasher timer which sold for only $60 and came with a free tool to adjust them, I just repaired the old timer with some knead it putty.

  25. #25
    Join Date
    Sep 2008
    Location
    India
    Age
    39
    Posts
    24
    Rep Power
    0

    Re: Differce of 50 hz and 60hz

    as frequency change the motor r.pm. will change.
    as the relation is given below..

    rpm= 120*frequency / no of pole.

Similar Threads

  1. 110v 60hz in a country w/ 220v 50hz
    By dkupinsky in forum Technical Speculations
    Replies: 22
    Last Post: 02-08-2010, 03:20 PM
  2. 50HZ compressor on a 60HZ circuit
    By dan wong in forum Technical Speculations
    Replies: 28
    Last Post: 13-06-2009, 05:52 PM
  3. 60Hz Copeland scroll compressor
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 05-06-2006, 09:08 PM
  4. Looking for 60hz appli in UK
    By nilechamp in forum Domestic
    Replies: 3
    Last Post: 27-01-2006, 08:40 AM
  5. 50Hz vs. 60Hz, okay to run at slower frequency?
    By pezagent in forum Commercial
    Replies: 10
    Last Post: 26-05-2003, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •