    cellar cooler fault.



    I have a beermaster cellar cooler running on 134a, looking at the sight glass seems the liquid level well below the line,

    in the cellar, the evaporator (very old, made by delta) seems the body and outlet pipe of the expansion valve gets iced up in approx 10 minutes after switching on, and leaving the evaporator not cold enough, this tells me that the refrigerant being too low causing pressure problem leading to the expansion valve to malfunction.. hence ice build up on the valve.

    AM i right ??
    as dont wanna evacuate the complete system to fit new expansion valve.

    Thanks



  2. #2
    Professor's Avatar
    Professor Guest

    Re: cellar cooler fault.

    Quote Originally Posted by fireblade View Post
    I have a beermaster cellar cooler running on 134a, looking at the sight glass seems the liquid level well below the line,

    in the cellar, the evaporator (very old, made by delta) seems the body and outlet pipe of the expansion valve gets iced up in approx 10 minutes after switching on, and leaving the evaporator not cold enough, this tells me that the refrigerant being too low causing pressure problem leading to the expansion valve to malfunction.. hence ice build up on the valve.

    AM i right ??

    as dont wanna evacuate the complete system to fit new expansion valve.

    Thanks
    Check the superheat setting on the valve body try turning the srcew fully in then undo 2.5 turns. Check to see if the last tubes in the evaporator are not iced up.

    All this is assuming the system is fully charged.

    Regards, Professor

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: cellar cooler fault.

    If you suspect that the refrigerant charge is low try a leak check of the system before you touch anything.

    If it came out once it will come out again.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: cellar cooler fault.

    Has it got a condeser fan speed controler? If its set wrong/ not fitted (fan running too quick causing low head pressure) can cause bubbles in the sight glass. Is the evaporator gummed up with mold and gunge causing low air flow. Low air flow = low load = frosty valve. Or it could just have a leak somewhere.

  5. #5
    Join Date
    Jul 2006
    Location
    uk
    Age
    58
    Posts
    14
    Rep Power
    0

    Re: cellar cooler fault.

    There is no fan speed controller, or defrost heaters, a very simple circuit, i will check for leaks while the system is running then i will switch the system off, wait a while then check the sight glass for correct level, as brian and monkey say, if the charge has gone, there has to be an exit.

    but on the whole do expansion valves need setting regulary if there is no other fault with the circuit ??

    thanks all.

    fireblade

  6. #6
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: cellar cooler fault.

    Hi It seems to me you have problem of starvation to thr TX valve, if I were you check back wards from the TX valve have you checked to see if the Compressor is pumping ie. broken valve reeds. Only a thought

    Regards Toosh

  7. #7
    Join Date
    Jul 2006
    Location
    uk
    Age
    58
    Posts
    14
    Rep Power
    0

    Re: cellar cooler fault.

    Thanks tosh..
    before the tx valve there is a solenoid valve, which is energised, i have to do a spot heat check, to ensure the valve is operating, and the temp is the same both sides if the soleniod valve,if so, then its got to be low charge, hoping its not the valves in the comp !!

    thanks
    fireblade

  8. #8
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: cellar cooler fault.

    try putting your gauges on,this normally helps

  9. #9
    eddiebee's Avatar
    eddiebee Guest

    Re: cellar cooler fault.

    Ill have a crack at this one, why not.

    From what you've said sounds like an old pump down system. The solenoid should be open. Wouldn't expect a compressor problem, no compression means no change of state and no duty from the gas - clearly if you get frost after the TEV you are getting compression and subcooling. I'd agree that it sounds like a starvation problem.

    My advice would be clear the evaporator of frost, stick the gauges on and check the superheat. If it's very high this would indicate an undercharge, possibly due to gas loss. You should never need to change the TEV setting really, assuming it was set up correctly, the whole point is that it's designed to maintain a constant level of superheat through the evaporator.

    Although if you like you could try winding it out to flood the evaporator. If you still get the frost, recover and check for leaks, start with the most obvious things - flared joints etc.

    hope this helps

  10. #10
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: cellar cooler fault.

    Quote Originally Posted by eddiebee View Post
    Wouldn't expect a compressor problem, no compression means no change of state and no duty from the gas - clearly if you get frost after the TEV you are getting compression and subcooling. I'd agree that it sounds like a starvation problem.
    I don't know what the problem is with out actualy fitting gauges and seeing it run.
    Your symptoms do point to lack of refrigerant though.

    But as for the comp sugestion it is feasable that the comp could have valve problems.
    The comp runs but gas passes back from the high side to low increasing the back pressure and reducing the discharge pressure.
    The symptons then become the same as the ones you have.

    taz.

  11. #11
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: cellar cooler fault.

    Quote Originally Posted by fireblade View Post
    There is no fan speed controller, or defrost heaters, a very simple circuit, i will check for leaks while the system is running then i will switch the system off, wait a while then check the sight glass for correct level,
    I'm a little worried here, are you using the sight glass as a liquid level indicator when the system is switched off?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  12. #12
    so-cold's Avatar
    so-cold Guest

    Re: cellar cooler fault.

    have you tried changing the drier .i had a problem like this a few years ago ,the drier was full of carbon ,and as soon as i replaced drier problem solved

  13. #13
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: cellar cooler fault.

    Yeah a blockage in the liquid line causes similar symptoms to a system short of refrigerant if just looking at a sightglass or pressures. Both give you a low sightglass and low suction pressure and discharge pressure.
    But normally you can find a temperature difference across a blockage, if it's a blocked drier, the drier outlet temperature would be slightly cooler than the inlet.

    Not to mention subcooling of the liquid line, the liquid temp after the condenser in a system short of refrigerant would be way hotter compared to the temp read off your gauge/PT chart than system with a blockage due to the backed up liquid in the coil.
    Last edited by paul_h; 11-07-2007 at 11:43 AM.

Similar Threads

  1. Searle cellar cooler
    By cold as ice in forum Technical Discussions
    Replies: 19
    Last Post: 13-01-2009, 01:09 PM
  2. cellar cooler with a/.c condenser
    By rbartlett in forum Air Conditioning
    Replies: 5
    Last Post: 01-03-2006, 10:56 PM
  3. Cellar cooler in the 'Vic
    By shanes696 in forum Commercial
    Replies: 6
    Last Post: 19-12-2005, 10:43 PM
  4. Searle cellar cooler control problem
    By iceman007 in forum Electrical
    Replies: 6
    Last Post: 06-07-2004, 08:57 PM
  5. IMI Marstair Cellar Cooler
    By Abe in forum Trouble Shooting
    Replies: 25
    Last Post: 20-03-2004, 02:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •