    Post suction accumulator control



    A industrial refrigeration design of mine utilses ammonia, screw compressors, evaporators, thermosyphon oil cooling, PHE and evaporative condersers.

    A ND100mm diameter pipe leads from the liquide receiver to the suction accumulator.

    A modulating liquid level regulator, servo controlled, danfoss PMFL125 was specified as the controlling for liquid injection into the suction accumulator.

    My questions:
    a) Could an electronic expansion valve (possible and AKVA20) of adequate size be utilised instead of the PMFL125?
    b) Would control be better utlising an eletronic expansion valves?
    c) What other forms of control are commonly utilised?

    Kind regards



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: suction accumulator control

    Welcome to the RE forums. It's nice to see another ammonia person on the site.

    I'm not familiar with the two controls you mentioned and would have to investigate them.

    Modulating control for liquid feed to a vessel for level control is the best method I believe as it does a better job of controlling the vessel pressure by reducing the pressure spikes.

    The only two other methods I have seen commonly seen are:
    1. low side float valves
    2. or a solenoid valve controlled by a level switch and a hand expansion valve
    If all else fails, ask for help.


  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: suction accumulator control

    This is an excellent forum. (I took a while to figure out how to post a message).

    I am fairly new to industrial refrigeration - less than 2 years and do not have a good feel for the systems yet.

    Thus I thought of geeting feedback of these two valves and experience in field. The main reason for selecting the modulating liquid level regulator (danfoss PMFL125) was to reduce the spikes.
    The only question now remain is - is the AKVA20 better...

    Back to the catalogues for me.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: suction accumulator control

    Quote Originally Posted by samiam
    Back to the catalogues for me.
    Don't give up yet.

    Some of the other ammonia people here may have some good comments!
    If all else fails, ask for help.


  5. #5
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: suction accumulator control

    Hi Samiam,

    I don't know if you know this book:

    http://www.ra.danfoss.com/TechnicalI...LA_version.pdf

    It also gives some examples on LP Liquid Level Regulation. (PMFL, AKVA, solenoid+regulating valve, motorised valve, ...); see page 31 and following.

    There is no clear answer to which is 'the best' way. A lot of this comes down to habbits.

    The valve itself is not the most important, but the combination of it with a mesuring/regulating device is. It's important to get a 'well tuned' combination. And this is possible with several combinations.
    Best regards.
    Last edited by BESC5240; 22-06-2007 at 08:15 AM.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: suction accumulator control

    Hi BESC5240,

    Thank you for posting the link to the book. This looks very interesting!

    Best regards,
    US Iceman
    If all else fails, ask for help.


  7. #7
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: suction accumulator control

    Hi,

    Thanks for the advice - I relooked at the problem and completed the suction accumulator control including the electronic signal interface with the transmitter, etc. This helped.


    Thanks again for the fedback and the link.

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. MP66 & Compressor Overheating
    By Intermez in forum Technical Discussions
    Replies: 111
    Last Post: 13-04-2010, 08:58 PM
  3. liquid injection triggered on low suction method
    By liptow in forum Fundamentals
    Replies: 10
    Last Post: 22-03-2007, 02:37 PM
  4. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  5. Suction temp
    By Temprite in forum Commercial
    Replies: 18
    Last Post: 30-05-2005, 10:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •