    Hi all;

    Iīve seen this term (re-heating coil) in an evaporatorīs catalogue as an optional. Can anybody tell me what that means?

    Best regards

    Miguel



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,058
    Rep Power
    24
    They are sometimes called terminal re-heat coils and are used in air conditioning applications where the evaporator's main duty is moisature removal.

    When the desired wet-bulb condition is achieved and to give the design relative humidity, the off coil dry bulb may be too low. heat is then added after the cooling coil to temper the delivery temperature. It is possible to have them both in operation at the same time
    It's not often used unless real humidity control is needed.

    The best illustration can be seen if you plot it on a psych chart.

    Sometimes an electric heating option is offered with some small split systems instead of cooling for the winter months. This is not the same thing.

    Hope it helps
    ________
    Yamaha Virago 750 history
    Last edited by Argus; 07-02-2011 at 08:48 AM.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,086
    Rep Power
    25
    Argus' reply is succinct and accurate. But here is perhaps another way to explain it, as one does often have to explain it to somebody not in the industry:

    When you want a lower RH than normal comfort cooling provides, you need to let the air conditioner run longer so it can continue to extract moisture even after the desired dry bulb (thermometer) temperature is achieved. By warming up the air after the air leaves the evaporator coil, the air conditioning unit can continue to run on its thermostat and wring more moisture out of the air that passes over it.

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    Not quite true Dan

    Reheat is used after cooling to bring either the temperature up because the cooling has reduced the temperature too much or it is used to expand the cool air to reduce the humidity (same moisture content in an expanded air volume = less humidity) - it doesn't really wring more moisture out! - just another way of saying the same thing!
    Last edited by frank; 30-08-2002 at 08:34 PM.

Similar Threads

  1. fresh air heating in cold area
    By Lc_shi in forum Air Conditioning
    Replies: 7
    Last Post: 14-05-2009, 01:37 AM
  2. air cooling and heating coil test
    By Lc_shi in forum Technical Speculations
    Replies: 8
    Last Post: 23-02-2006, 02:15 AM
  3. heating coil in front of duct unit
    By cruzeiros in forum Air Conditioning
    Replies: 3
    Last Post: 14-02-2006, 12:32 AM
  4. Burst Coil
    By frank in forum Air Conditioning
    Replies: 13
    Last Post: 20-02-2005, 07:28 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •