    Cool E0 error code daikin vrv



    Hello engineers,
    on a RNY10K7W1 VRV DAIKIN (double condensing unit) randomly appears on indoor displays the E0 error code, which is known to be the activation of a not well specified "safety device" on the outdoor unit.
    Resetting the fault produces the effect of let start only B outdoor units... Even though load request is maximum (setting all indoors at 16 centigrade) unit A is completely silent and no error detection is shown either on the main board or the indoor displays. Nothing seems to be wrong, except that after a X period of time (hours), the E0 flashes again and everything doesn't run.
    Tried to disconnect both condenser fans (one by one) and nothing changes.
    Anyone already had such trouble sometimes?
    Thank you for your help.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: E0 error code daikin vrv

    The rny10 is a single unit. do you mean you have 2 of these coupled together making a rny20?

    The EO fault code relates to either the fan thermal protection device or the compresor overload.

    One thing to remember - if the code shows then the fault is definately there.

    Nothing seems to be wrong, except that after a X period of time (hours), the E0 flashes again and everything doesn't run.
    Seems that one of the secondary compressors may be suspect. We had a similar fault related to an undersized crankcase heater (40W instead of 70W) which eventually led to a lost compressor due to lack of oil.

    As it was always the last compressor to be called under high load conditions it used to run with a low oil level. Daikin are aware of this and they paid our time and materials to correct it.

  3. #3
    Join Date
    Dec 2001
    Location
    Italy
    Posts
    19
    Rep Power
    0

    Re: E0 error code daikin vrv

    Got it!
    It was a bloody fan.. It was kidding me, but thanks to your suggestions I could detect it. Thanks a lot, frank!

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. DAIKIN - Weybridge: How to get a Quote.
    By Makeit go Right in forum Air Conditioning
    Replies: 12
    Last Post: 25-04-2007, 08:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •