19-06-2007, 03:45 PM #1
Hello engineers,
on a RNY10K7W1 VRV DAIKIN (double condensing unit) randomly appears on indoor displays the E0 error code, which is known to be the activation of a not well specified "safety device" on the outdoor unit.
Resetting the fault produces the effect of let start only B outdoor units... Even though load request is maximum (setting all indoors at 16 centigrade) unit A is completely silent and no error detection is shown either on the main board or the indoor displays. Nothing seems to be wrong, except that after a X period of time (hours), the E0 flashes again and everything doesn't run.
Tried to disconnect both condenser fans (one by one) and nothing changes.
Anyone already had such trouble sometimes?
Thank you for your help.
19-06-2007, 08:44 PM #2
Re: E0 error code daikin vrv
The rny10 is a single unit. do you mean you have 2 of these coupled together making a rny20?
The EO fault code relates to either the fan thermal protection device or the compresor overload.
One thing to remember - if the code shows then the fault is definately there.
As it was always the last compressor to be called under high load conditions it used to run with a low oil level. Daikin are aware of this and they paid our time and materials to correct it.
21-06-2007, 03:55 PM #3
Got it!
It was a bloody fan.. It was kidding me, but thanks to your suggestions I could detect it. Thanks a lot, frank!
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin, Why do we bother?
By gwilliamson in forum Air ConditioningReplies: 21Last Post: 02-02-2010, 09:38 AM -
Daikin Analyzer
By marc5180 in forum FundamentalsReplies: 10Last Post: 02-08-2008, 07:15 PM -
Daikin Controllers
By airefresco in forum Air ConditioningReplies: 5Last Post: 15-05-2008, 08:08 AM -
DAIKIN - Weybridge: How to get a Quote.
By Makeit go Right in forum Air ConditioningReplies: 12Last Post: 25-04-2007, 08:50 PM