I'm really stuck on a question and wondered if anyone has the knowledge to help me??
"List 5 indicators used to confirm that a system is correctly charged?"
Much thanks.
17-06-2007, 06:07 PM #2
Re: HELP NEEDED a.s.a.p :)
Hi mather and welcome,
In my opinion they are as follows :
1- LP = suction pressure
2- HP = discharge pressure
3- SH = super heat
4- SC = sub-cooling
5- Bubbles in the sight glass
CheersEven Einstein Asked Questions
17-06-2007, 06:13 PM #3
Ohh, cheating for a test are we??
-Sight-glass
-Sub cooling
-Liquid receiver's liquid level
The above are the best I can think of at the moment, below are secondary ones.
-Super heat
-Discharge temperature
-Delta T between discharge and liquid
-Compressor running current (most noticeable on inverter driven compressors in VRV/VRF systems)
-Delta T across evaporator
17-06-2007, 08:20 PM #4
cheers guys...
30-06-2007, 01:40 PM #5
id list them as
Superheat
Subcooling
High Pressure
Low Pressure
Air temperatures
Pipe temperatures
30-06-2007, 04:40 PM #6
You could also add
Correct charge weight.
Customer satisfactionBrian - Newton Abbot, Devon, UK
01-07-2007, 05:59 AM #7
Compressor running
Condenser delta-T
Evaporator delta-T
Subcooling
Superheat
01-07-2007, 10:11 AM #8
ishould of joined this site when i was on my college course hehe
02-07-2007, 03:22 PM #9
BTW, you are apparently being taught backwards troubleshooting. Out there in the real world you are not given the problem and asked the symptoms, you are given the symptoms and asked the problem.
03-07-2007, 08:58 AM #10
Acheiving temps ???
Paula
03-07-2007, 12:11 PM #11
Well Said Gary!
04-07-2007, 06:54 PM #12
Re: Help needed
customer offers you a drink?
never happen when its not workingPaul
"KEEP IT COOL"
24-07-2007, 04:27 PM #13
This is more important than many would believe. People form habits in school which are extremely difficult to change. They go through life troubleshooting backwards, i.e. suspecting what the problem might be and then seeing if the symptoms match, rather than checking the symptoms and then narrowing down to the problem(s).
Autocascade refrigeration system: design verification needed
By DaBit in forum Technical SpeculationsReplies: 3Last Post: 07-02-2010, 07:48 AM -
Carrier 40GKX028 service manual needed
By Ireland in forum Air ConditioningReplies: 6Last Post: 08-02-2007, 07:06 PM -
help needed
By Leo1967 in forum Technical DiscussionsReplies: 8Last Post: 12-08-2004, 06:07 PM -
Double check needed
By Latte in forum Trouble ShootingReplies: 14Last Post: 11-08-2004, 12:46 PM -
How many small strands needed to equal pipe pressure drop?
By DaBit in forum FundamentalsReplies: 17Last Post: 25-08-2003, 09:56 PM