    internal thermo switch



    hi, i was wondering can someone explain why a compressors internal thermo strip may activate..even though.. the gas charge is ok.. compressor mechanical parts ok..all others like fans coils etc are ok..and installation in general seemed good..have come across this on some compresssors!

    cheers



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: internal thermo switch

    It is probably going O/C because of high current.

    Check the resistance of the windings according to the manufacturers specification.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: internal thermo switch

    Quote Originally Posted by chillin out View Post
    It is probably going O/C because of high current.

    Check the resistance of the windings according to the manufacturers specification.

    Chillin
    hi chill,ye have done that before all windings balanced,however a little leakage to earth,was wondering does current get drawn from the slight grounding in some way???

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: internal thermo switch

    Those are heat sensitive, so look for things that might contribute to higher than normal heat.

    High suction superheat
    high discharge pressures
    broken discharge valves will add a lot of heat
    low voltage
    loose connections on motor or starter

    Those are some quick things I can think of.
    If all else fails, ask for help.


  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: internal thermo switch

    Quote Originally Posted by philjd26 View Post
    hi, i was wondering can someone explain why a compressors internal thermo strip may activate..even though.. the gas charge is ok.. compressor mechanical parts ok..all others like fans coils etc are ok..and installation in general seemed good..have come across this on some compresssors!

    cheers
    Most compressor motors are wound with a thermal sensor in each phase, so a 3 pase comp has three in series wound deep into the windings.
    If as you say everything is fine with the comp then I would check the thermistor modual itself.
    They have an internal relay that can fail.
    With normal running they can trip and then once the comp has been reset they run as if there was no problem.
    If in doubt and if you have proved all is well with the comp then change the thermistor modual.

    taz.

  6. #6
    Join Date
    Jan 2007
    Location
    Chesterfield, UK
    Posts
    79
    Rep Power
    18

    Re: internal thermo switch

    Is it a Maneurop compressor?

    They need some cool gas back to stop them overheating.

    Earth leakage is unlikely, 1000v megga test it though.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: internal thermo switch

    Quote Originally Posted by Dr._Fleck View Post
    Is it a Maneurop compressor?

    They need some cool gas back to stop them overheating.
    All compressors need this

  8. #8
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: internal thermo switch

    I think he meant that maneurop rely on some liquid returning to the comp to keep it within working specs.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  9. #9
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: internal thermo switch

    Thanks for the comments lads.but sorry forgot to mention that these compressor i come across are inverter driven, and has a thermo switch connections on the shell with phase connecrtings...compressor runs for a while however not 100%... could it be the high volts/frequencey when looking for more duty that makes thermo open....all conditions i said at the start still apply another words every thing seems to be good however slight grounding..

  10. #10
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: internal thermo switch

    Quote Originally Posted by philjd26 View Post

    ..

    It's not a klixon is it?
    Klixons will activate if the running amps go up not just temp.

    taz.

  11. #11
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: internal thermo switch

    there fitted for two things,over current and overheat,or on three phase machines ,mainley over temp,unless its something like a star point protector[old stuff now] witch does both on most machines ,over about 1 horspower most have contactors and overload units for overcurrent protection/phase loss and if the compressor is stressed and getting hot the current should go up anyway and trip,no expert on inverter yet as not had many breakdown, there are inverter checkers available now but make sure the systems good first. could be a long thread this as theres to much to say in one go !

  12. #12
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: internal thermo switch

    It could be due to high discharge superheat if it is mounted on the compressor body. In many ac compressors the body is open to discharge pressure and temperature, this is why they often run very hot to the touch, this is done to use the compressor body as a discharge muffler to keep the noise down.
    The manufacturer should be able to tell you what temperature it should switch at, you can then check this with an infra red thermometer. Maybe the thermal overload is faulty.

    Cheers Jon

  13. #13
    Join Date
    Feb 2007
    Location
    SIDE OF THE ROAD
    Posts
    262
    Rep Power
    18

    Re: internal thermo switch

    thanks for the comments... was also wondering what is the name for the waxy stuff that motors are wound in,and any ideas what makes this stuff break down apart from moisture and heat,........

    cheers

Similar Threads

  1. flow switch connection
    By afeef in forum The Trail of Tears
    Replies: 18
    Last Post: 23-12-2009, 06:55 PM
  2. Low Pressure Cut-off switch on Liquid line
    By Vishnukurup in forum Air Conditioning
    Replies: 14
    Last Post: 03-12-2008, 09:34 AM
  3. thermo acoustic refrigerator: problem with stack heating
    By jackal in forum Technical Discussions
    Replies: 6
    Last Post: 04-09-2006, 05:03 PM
  4. Thermo King v? 00 MAX Tc Wiring Diagram
    By Chris2005 in forum Transport
    Replies: 3
    Last Post: 01-02-2006, 08:01 AM
  5. shower switch fault !
    By Krups in forum Electrical
    Replies: 10
    Last Post: 19-10-2005, 09:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •