    Daikin VRV Fault



    Hey guys, I have a Daikin Rsey10gk7w1 outdoor that a previous company changed a condenser fan motor on,iv been called to site to check this out after they got arsed out..
    Im getting an E0 fault,im aware this is a safety device fault and have checked continuity thru cn2-cn7.. iv found cn4( which comes from the new fan motor) to be open circut..
    Iv linked out cn4 at present so at least it runs..
    any daikin lovers out there any ideas..

    cheers
    justin



  2. #2
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    124
    Rep Power
    18

    Re: Daikin VRV Fault

    HI there, you should have 240v going through the gray wires(overloads) to your fan motors.Had a lot of problems with these fan motors blowing due to water getting in..Would also check HP /LP switches. Happy hunting.

  3. #3
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin VRV Fault

    Quote Originally Posted by licencetochill View Post
    Hey guys, I have a Daikin Rsey10gk7w1 outdoor that a previous company changed a condenser fan motor on,iv been called to site to check this out after they got arsed out..
    Im getting an E0 fault,im aware this is a safety device fault and have checked continuity thru cn2-cn7.. iv found cn4( which comes from the new fan motor) to be open circut..
    Iv linked out cn4 at present so at least it runs..
    any daikin lovers out there any ideas..

    cheers
    justin
    Strange from a new fan motor...
    Had a lot of other problems on these old series but not this kind.
    In France we had faulty motors on R407C series.
    rgds
    cool#9

  4. #4
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Cool Re: Daikin VRV Fault

    Maybe they didnt change the ventilator.

    Best regards,
    Renato

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Daikin fault codes
    By Markie in forum Air Conditioning
    Replies: 16
    Last Post: 13-01-2009, 01:58 AM
  3. Daikin FUYP71BV1 fault code
    By Andy W in forum Air Conditioning
    Replies: 6
    Last Post: 15-02-2007, 09:11 PM
  4. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM
  5. daikin AF fault
    By rbartlett in forum Air Conditioning
    Replies: 5
    Last Post: 27-07-2006, 09:01 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •