    High Freezer temperature



    Hi

    I have a walkin freezer which used to operate at about -18degC. the owners shut it down to have a new floor laid, now its been switched back on, the temperature in the room does not drop below minus12degC. the system is running on R22 suction pressure of 21psi discharge pressure seems a bit low around 150psi subcooling very good and with a clear sight glass, superheat around 8degC, The evaporator is clean, clear and not icing up, i've tried opening the TEV and shutting the TEV, neither seemed to have much effect.

    Any ideas??????????

    CB



  2. #2
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: High Freezer temperature

    Compressor or low on gas

    Paula

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: High Freezer temperature

    Hi

    I've checked the compressor (had the head of and check pistons and valves/plate) all perfect. gas charge seems fine too!.

    I think the system is undersized

    CB

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: High Freezer temperature

    when its had a new floor laid it should be bought down in stages over a week, 1=+4, 2= -5ish, then let in go at its target temp,there will be alot of heat to come out of the new floor,as said, one week, if it dont make it soon after that start looking at undersize kit or fault finding. they did renew the floor insulation ? yes.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    20

    Re: High Freezer temperature

    The system may be low on gas. But asw Old Gas Bottle says, if the floor has been laid a fresh, then give it some time and also check the floor insulation.

  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: High Freezer temperature

    Hi everybody,

    I do agree with old gas bottle as long as there is no refrigeration problem.

    Check the attached file.

    Cheers
    Attached Files Attached Files
    Even Einstein Asked Questions

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: High Freezer temperature

    If it is concrete, then you have to wait 28 days before freezing.
    Good link Lana, thanks
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: High Freezer temperature

    Quote Originally Posted by chillyblue View Post
    Hi

    I have a walkin freezer which used to operate at about -18degC. the owners shut it down to have a new floor laid, now its been switched back on, the temperature in the room does not drop below minus12degC. the system is running on R22 suction pressure of 21psi discharge pressure seems a bit low around 150psi subcooling very good and with a clear sight glass, superheat around 8degC, The evaporator is clean, clear and not icing up, i've tried opening the TEV and shutting the TEV, neither seemed to have much effect.

    Any ideas??????????

    CB
    Had the same problem with a freezer room which had a new condensing unit installed.

    Told customer that original unit was undersized but he insisted on changing with a unit of similar capacity.

    The walls of the room were water logged also,and unit was turned off for about a one week period.

    Unit got to about -12 degrees c and stayed there for about a week, after that it pulled down to the correct temp.

  9. #9
    Join Date
    Jul 2006
    Location
    USA
    Age
    74
    Posts
    865
    Rep Power
    26

    Re: High Freezer temperature

    Quote Originally Posted by Temprite View Post
    Had the same problem with a freezer room which had a new condensing unit installed.
    Unit got to about -12 degrees c and stayed there for about a week, after that it pulled down to the correct temp.
    This is something I have seen many times in Blast Freezers. They typically have no source of cooling except for the Blast Coil, and are operated seasonally.
    On startup for the season, it would take a couple of days for the heat to come out of the floor, and normal operation to resume.
    Please note that these freezers I refer to had no insulation in the floor.
    I have also seen this in Spiral Freezers with water saturated Fiberglass insulation in the floor.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  3. Replies: 1
    Last Post: 03-04-2006, 09:18 AM
  4. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •