14-06-2007, 08:59 AM #1
High Freezer temperature
Hi
I have a walkin freezer which used to operate at about -18degC. the owners shut it down to have a new floor laid, now its been switched back on, the temperature in the room does not drop below minus12degC. the system is running on R22 suction pressure of 21psi discharge pressure seems a bit low around 150psi subcooling very good and with a clear sight glass, superheat around 8degC, The evaporator is clean, clear and not icing up, i've tried opening the TEV and shutting the TEV, neither seemed to have much effect.
Any ideas??????????
CB
-
14-06-2007, 09:38 AM #2
Re: High Freezer temperature
Compressor or low on gas
Paula
-
15-06-2007, 02:39 PM #3
Re: High Freezer temperature
Hi
I've checked the compressor (had the head of and check pistons and valves/plate) all perfect. gas charge seems fine too!.
I think the system is undersized
CB
-
15-06-2007, 05:21 PM #4
Re: High Freezer temperature
when its had a new floor laid it should be bought down in stages over a week, 1=+4, 2= -5ish, then let in go at its target temp,there will be alot of heat to come out of the new floor,as said, one week, if it dont make it soon after that start looking at undersize kit or fault finding. they did renew the floor insulation ? yes.
-
15-06-2007, 05:25 PM #5
Re: High Freezer temperature
The system may be low on gas. But asw Old Gas Bottle says, if the floor has been laid a fresh, then give it some time and also check the floor insulation.
-
15-06-2007, 05:45 PM #6
Re: High Freezer temperature
Hi everybody,
I do agree with old gas bottle as long as there is no refrigeration problem.
Check the attached file.
CheersEven Einstein Asked Questions
-
16-06-2007, 06:12 PM #7
Re: High Freezer temperature
If it is concrete, then you have to wait 28 days before freezing.
Good link Lana, thanksIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
17-06-2007, 01:33 PM #8
Re: High Freezer temperature
Had the same problem with a freezer room which had a new condensing unit installed.
Told customer that original unit was undersized but he insisted on changing with a unit of similar capacity.
The walls of the room were water logged also,and unit was turned off for about a one week period.
Unit got to about -12 degrees c and stayed there for about a week, after that it pulled down to the correct temp.
-
17-06-2007, 02:50 PM #9
Re: High Freezer temperature
This is something I have seen many times in Blast Freezers. They typically have no source of cooling except for the Blast Coil, and are operated seasonally.
On startup for the season, it would take a couple of days for the heat to come out of the floor, and normal operation to resume.
Please note that these freezers I refer to had no insulation in the floor.
I have also seen this in Spiral Freezers with water saturated Fiberglass insulation in the floor.
Similar Threads
-
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
fun quiz
By Brian23 in forum New to REReplies: 6Last Post: 02-10-2007, 10:18 PM -
an environmentally friendly high temperature refrigerant
By star882 in forum RefrigerantsReplies: 1Last Post: 03-04-2006, 09:18 AM -
Q=? h1=? mechanical schematics
By fridg in forum Technical SpeculationsReplies: 22Last Post: 19-03-2006, 01:43 PM -
Article in ACH&R News
By Gary in forum FundamentalsReplies: 8Last Post: 20-05-2003, 12:27 AM