    Re: Evaporating / condensing temperatures

    Quote Originally Posted by lana View Post
    Dear Mehamed,

    If smaller condenser is selected then for 3 days in a year this will cause the condensing pressure to rise and therefore, more energy will be wasted.

    Cheers
    Ok i forgot to tell u i clarified that in the example i gave to Ravi when i told him my design tends to consume a larger energy and of course more expensive energy bill in the three days but on the other days the design will be favorable in terms of energy consumption and bill. Kindly refer to this post and read it carefully.

    Cheers

  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Evaporating / condensing temperatures

    Hi Mohamed,

    Again we are saying the same thing.

    Ambient = hot --TDc = small -- Cond. surface = big -- Cond. pressure = good -- Energy consumption = good

    Ambient = cold -- TDc = large -- Cond. surface = small -- Cond. pressure = good -- Energy consumption = good

    If your concern is energy consumption then you have to design a condenser which gives lower condensing pressure.

    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Evaporating / condensing temperatures

    Quote Originally Posted by lana View Post
    Hi Mohamed,

    Again we are saying the same thing.

    Ambient = hot --TDc = small -- Cond. surface = big -- Cond. pressure = good -- Energy consumption = good

    Ambient = cold -- TDc = large -- Cond. surface = small -- Cond. pressure = good -- Energy consumption = good

    If your concern is energy consumption then you have to design a condenser which gives lower condensing pressure.

    Cheers
    Hi Lana

    Thanks Lana for this good demonstration

    Cheers

Similar Threads

  1. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  2. This a long one - AKV
    By Peter_1 in forum Industrial
    Replies: 6
    Last Post: 26-12-2008, 11:47 AM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. evaporating temperatures
    By MrsFreeze in forum Fundamentals
    Replies: 11
    Last Post: 31-05-2007, 02:15 AM
  5. Condensing temperatures with ammonia
    By Friobernal in forum Technical Discussions
    Replies: 2
    Last Post: 12-07-2002, 02:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •