    TX adjustment



    I have a 25 HP copeland , using HP 80 , The suction is 5 psi . the temperature is 33 F on the suction side at the compressor ( I can't get at the evaporator without removing product) . the discharge pressure is OK but the temperature is a little high . I was going to open the TX valve a little more . should I check anything else before I start crawling over 10,000 pounds of half frozen fish.



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: TX adjustment

    HP 80 is R402a, 5 psi = 0,3 bar, 33F is 0,5 dgrC. So the superheat is 42K!

    How high is the discharge temp and what pressure? Liquid line temp and subcool?

    Perhaps lacking refrigerant?

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: TX adjustment

    Quote Originally Posted by claude11 View Post
    I have a 25 HP copeland , using HP 80 , The suction is 5 psi . the temperature is 33 F on the suction side at the compressor ( I can't get at the evaporator without removing product) . the discharge pressure is OK but the temperature is a little high . I was going to open the TX valve a little more . should I check anything else before I start crawling over 10,000 pounds of half frozen fish.
    Hi claude11

    U have an oil separator in ur system or not? ...if it is not, it may sound there is an excess amount of oil in ur system causes some blockage in the TXV and inefficient operation of the evaporator as well the raising in discharge temperature. Otherwise check the subcooling, the filter-drier and receiver. I wish it could help

    Cheers

  4. #4
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: TX adjustment

    Hi there,

    Before adjusting the TEV check the followings :
    Super heat
    Sub cooling
    LP
    HP

    If low pressure is low and super heat is high and sub cooling is OK then check for any blockage in the liquid line first. If any thing is OK then it is the TEV.

    If low pressure is low and super heat is high and sub cooling is low then there is lack of refrigerant.

    If low pressure is low and super heat is low then check your evaporator. Look for anything which prevents evaporation, like fans are working , frost ,...

    Hope this helps
    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. T.E.V. adjustment.
    By FreezerGeezer in forum Ye Old Wifes Tales
    Replies: 46
    Last Post: 22-06-2010, 11:58 PM
  2. Liguid Injection Temperature Adjustment
    By NH3LVR in forum Industrial Compressors
    Replies: 4
    Last Post: 06-12-2006, 04:41 PM
  3. R410A compressor - capacity adjustment
    By Stans in forum Commercial
    Replies: 7
    Last Post: 14-09-2006, 03:49 AM
  4. Expantion valve adjustment
    By ayaz in forum Technical Speculations
    Replies: 5
    Last Post: 22-04-2006, 03:43 PM
  5. Pressure control adjustment and Case temperatures
    By mccoolair@yahoo in forum Supermarket Refrigeration
    Replies: 3
    Last Post: 08-04-2006, 12:21 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •