    Question Suction Accumulators



    Whilst estimating the holding capacity of an Accumulator, is the entire internal volume of the accumulator considered or about 75 to 80% as is normally done for a Cylinder? The volume would be multiplied by the density of the liquid refrigerant at the evaporating temperature, I presume , to arrive at the weight of the refrigerant.
    I would like to know if this assumption is correct.
    Also, the weight calculated as mentioned above would be about 50% of the refrigerant charge inthe system, as recommended in most manufacturer tables. Some manufacturers talk of 65 or 70 % . What would be appropriate and what is the rationale behind this percentage factor?



  2. #2
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Re: Suction Accumulators

    Quote Originally Posted by rsiyer View Post
    Whilst estimating the holding capacity of an Accumulator, is the entire internal volume of the accumulator considered or about 75 to 80% as is normally done for a Cylinder? The volume would be multiplied by the density of the liquid refrigerant at the evaporating temperature, I presume , to arrive at the weight of the refrigerant.
    I would like to know if this assumption is correct.
    Also, the weight calculated as mentioned above would be about 50% of the refrigerant charge inthe system, as recommended in most manufacturer tables. Some manufacturers talk of 65 or 70 % . What would be appropriate and what is the rationale behind this percentage factor?
    Some designers would like to have the accumulator sized for almost 100% of system refrigerant charge on small systems and 80% of system refrigerant charge on large systems. The larger is the better for the accumulator this prevents liquid slugging back to the compressor provided it does not cause a severe pressure drop in suction line.

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: Suction Accumulators

    The usable volume of an accumulator is limited by how much liquid level it can carry and provide proper separation distance and separation velocity. It also depends whether the accumulator is vertical or horizontal and how many outlets are onthe accumulator.

    There is a chapter in the ASHRAE handbooks on designing accumulators. The maximum separation velocity is determined by Stoke's Equtions which considers the relative density of the liquid and vapor phases and the surace tension of the liquid.

    The whole idea of the accumulator is based on keeping liquid slugs and upsets out of the compressor suction. The accumulator should run dry and only have liquid in an up set.

    To aide in emptying the accumulator, you can run a liquid coil (called a boil-out coil) fed by the high pressure liquid and then on to the evaporator. During normal operation, with a dry vessel, the vapor superheat and subcooling in minimal. If you have liquid there, the hot liquid will boil off the liquid in the vessel and subcool the liquid in the coil. The net effect on the system performance is close to zero.

    Suction accumulator design is a whole different topic that can cover a lot of different designs and applications.
    Ken

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. liquid injection triggered on low suction method
    By liptow in forum Fundamentals
    Replies: 10
    Last Post: 22-03-2007, 03:37 PM
  3. Replies: 10
    Last Post: 18-03-2006, 08:35 PM
  4. Measure suction line pressure drop with thermometer
    By Steve Wright in forum Fundamentals
    Replies: 7
    Last Post: 17-09-2005, 11:05 PM
  5. Suction temp
    By Temprite in forum Commercial
    Replies: 18
    Last Post: 30-05-2005, 10:33 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •