Thread: Fault finding

  1. #1
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Fault finding



    Hi guys been called to a Airedale unit tomorrow that for some reason wont even come on. Can anyone give me any fault finding tips i.e electrical. The first things you should check when the units wont start because i know on Airedales you dont get given fault codes.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Fault finding

    Do we know which model or type it is yet?

    It may have electronic or mechanical controls.

    I suppose check power, pressure switches, delay timers.

    You never know it just be simply 'broke'
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Unhappy Re: Fault finding

    Quote Originally Posted by Brian_UK View Post
    Do we know which model or type it is yet?

    It may have electronic or mechanical controls.

    I suppose check power, pressure switches, delay timers.

    You never know it just be simply 'broke'
    All i know is that it has an airedale condensing unit with an indoor AHU controlled by a trend controller, with an EEV and a few solonoids. One of the engineers went to it the other day...found a leak, repaired it but he couldnt get it to come back on. I asked if he had turned the temp down on the controller but he said he couldnt get into it. So thats why im looking for help on fault finding cos the control circuit ialways seems to baffle me.

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fault finding

    Aha, it's Trend controlled, has been in alarm (fault) mode, been repaired and now not starting.

    Most Trend systems will monitor alarms or faults (your LP switch for example) then, depending on the trend's setup, it will not ask for your unit to run again until the alarm been reset in the Trend.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault finding

    Is there normally a code to get into these trend controllers or not? its just that the other engineer had problems getting into it.

  6. #6
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fault finding

    BTW, to prove or dismiss this;

    The Trend's outstation is only a bank of relays, you will find two terminals in the controls of your unit (remote ON/OFF, remote enabling or the like) going to the Trend (there might be others on the alarm side of things but ignore them for now) short these two terminals and your unit should start if it's the Trend holding it Off.
    The above assumes that there is a "local" control in the A/C unit, otherwise there will be individual terminals for the fan, the compressor, the reversing valve and so on....

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Fault finding

    Yes, there is a code.

    BUT,

    It's set by the commissioning engineer, so no standard codes.
    If you are a registered Trend company you can call them and tell them what the time/date is on the display and they will give you a code that will work for an hour or so.

  8. #8
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault finding

    OK il try this first thing tomorrow and post back tomorrow evening. Thanks for your help

  9. #9
    Join Date
    Mar 2005
    Location
    Birmingham U.K.
    Age
    70
    Posts
    54
    Rep Power
    20

    Re: Fault finding

    Re Fault finding

    Airedales first level code is always 4648
    try this to alter temperature set points etc

    If it is in a computer/server room we always set everthing for auto restart after the electrical power is restored, so try just switching on at the mains isolator and it may just reboot.

    If it is comfort cooling you may have to enter the Trend software to reset the air flow switch etc.

    Airedale tel no is 01132391000 give them the unit type and the Unumber and they will talk you through the trend controls.

    Bob

  10. #10
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault finding

    Quote Originally Posted by bobjob View Post
    Re Fault finding

    Airedales first level code is always 4648
    try this to alter temperature set points etc

    If it is in a computer/server room we always set everthing for auto restart after the electrical power is restored, so try just switching on at the mains isolator and it may just reboot.

    If it is comfort cooling you may have to enter the Trend software to reset the air flow switch etc.

    Airedale tel no is 01132391000 give them the unit type and the Unumber and they will talk you through the trend controls.

    Bob
    Thanks for the info Bob il let you know how i get on.

  11. #11
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: Fault finding

    Hp,Lp,Oil etc.
    Airedale use a latching relay for the control circuit (at fault) quite a lot on standard CU units, pull all the relays out of the holders and replace. Difficult to tell without seeing it.
    Takes a licking, keeps on ticking.

  12. #12
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Fault finding

    Forgot that i had posted this, iv been back today to the unit and iv posted what i found today here....


    http://www.refrigeration-engineer.co...ead.php?t=8383

  13. #13
    Join Date
    Feb 2008
    Location
    Wellingborough
    Age
    56
    Posts
    35
    Rep Power
    0

    Re: Fault finding

    I appreciate that my reply may be somewhat late on this subject, but Airedale units with a Trend controller typically have a software switch (from memory, it may be switch 12) that needs user intervention following an airflow failure alarm.

    If the unit has failed on airflow, the unit will not re-start without this switch setting being changed.

    Also, regarding the PIN, as previously posted, Airedale's standard Trend PIN was 4648 which I think gave level 99 access (highest level). To be clear, this is a standard Trend code for Airedale units fitted with an IQ204 as it used to get a helpful mention in their manuals at the time.

    If that number has changed & you have access to either a Trend System House or Trend System Integrator, you will have use of PIN of the day. To use that, you need to have the firmware version of the Trend controller & what day/date/time the controller thinks it is (not necessarily what the actual day/date/time is!). Depending on the firmware, the PIN of the day that goes with your controller is vcalid for that day, however is accurate within plus or minus 5 digits of the actual number.

    You also get access to PIN of the day if you are Trend trained & hold a valid PNet card as I do.

    I don't believe that Airedale now fit Trend as standard.

Similar Threads

  1. Web Based Fault Finding
    By Brian_UK in forum Training
    Replies: 6
    Last Post: 20-05-2007, 08:18 PM
  2. lg fridge/freezer fault light on function display board
    By bazza in forum Trouble Shooting
    Replies: 0
    Last Post: 25-02-2007, 03:25 PM
  3. u4 fault on a Daikin inverter
    By phil17 in forum Air Conditioning
    Replies: 39
    Last Post: 05-02-2007, 02:41 AM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •