    Choosing between CO2, NH3 and GLYCOL circulation



    Having to build a new 12.000 m² fresh warehouse (2°C for meat and dairy) I have contacted three refrigeration companies.

    One company tells me to go for NH3
    The second one tells me to go for CO2
    And the third, you guessed it, suggests Glycol

    They all have valid points. Can you point me to some documentation that could help me choose between the alternatives?

    Thak you very much



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Hi Renaud,

    Welcome to the RE forums.

    This will be a thread I will follow closely. I do not have any documentation on the subject, but do think this will be an interesting discussion.

    A point I can raise now is; have the contractors provided any estimated operating costs to you? I would consider asking them to furnish this information for summer and winter periods. This will supply you with some basic information that you can use in your evaluation of the proposals.

    If the average operating cost is "x" Euros per month, then you can compare this to 12.000 m² and then also your initial costs too.

    Therefore you will find; "x" Euros/m² for operating and initial costs.

    I would also ask them how they are controlling your system too. Do they have control systems they will provide and how will the control system save you operating costs.
    Last edited by US Iceman; 06-06-2007 at 04:03 PM. Reason: text correction
    If all else fails, ask for help.


  3. #3
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Wink Re: Choosing between CO2, NH3 and GLYCOL circulation

    Find someone who will design system for you and than ask offer, that way you get best result.If you pay consultant he will calculate all you want:electric consumption,spare part availybility,competence of instolers etc.and you can go on tenis during that period.

    Best regards,
    Renato

  4. #4
    Join Date
    Jun 2007
    Location
    Belgium
    Posts
    5
    Rep Power
    0

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    As of now we have only had preliminary discussions with the three companies, where we talked over the project and gave them the plans. We have asked them to give us a preliminary study and budget in order to decide with which company to go further into the full study (for which we will pay of course).

    Some "figures" I have received for operating costs:
    Ammonia : 100%
    CO2 : 108%
    Glycol : 130%

    investment is the highest for glycol

    We have asked the companies to hand in some figures and first sketches for the end of the week but I doubt I will be able to choose with which company we would want to work with solely based on what they will hand in.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    I can't see how glycol system TCO can cost 30% more than nh3.

  6. #6
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    I would like know that for the Glycol System, how do they propose to chill Glycol. Either it would be with a NH3 or a CO2 refrigeration system. Am I correct or if I am wrong please do correct me.

    With whatever I have learnt from this Forum, I feel using NH# would be the best way.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Glycol brine is chilled with a standard chiller, probably using a HFC refrigerant.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Quote Originally Posted by Renaud
    We have asked them to give us a preliminary study and budget...
    That I think is a good business practice. You really need to understand what you are buying and how much it will cost to operate.

    Is the CO2 system also using ammonia, or only CO2?

    If you are anticipating using the CO2 or glycol options I suggest you ask them how they plan to defrost the evaporator coils. If they use electric defrost for either of these two options, have they included the electricity for defrost in their operating costs.

    Or, if they suggest water defrost have they included water usage and associated charges?

    Quote Originally Posted by Renaud
    Some "figures" I have received for operating costs:
    Ammonia : 100%
    CO2 : 108%
    Glycol : 130%
    Are these operating costs or investment costs?
    If all else fails, ask for help.


  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Here are some links I found that may be useful to you. These are both related to the same project, but it closely mirrors your requirements I believe.

    http://www.mmrefrigeration.com/mmsit...%20Systems.pdf
    (0.7 MB)

    http://www.ra.danfoss.com/TechnicalI...oldstorage.pdf
    (2.9 MB)
    If all else fails, ask for help.


  10. #10
    Join Date
    Jun 2007
    Location
    Belgium
    Posts
    5
    Rep Power
    0

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Thank you for your links I will read this for sure.

    To answer some of the questions above:
    The refrigeration will be done through NH3, this is certain. Only the circulation is problematic.
    The figures that were given to me are for operating costs only. I don't know how they were reached exactly but was promised some literature on the matter so I will get back to you once I get it.
    The three companies we contacted all design and install alls sorts of systems but they are not manufacturers and are not tied to a particular technology. They are all speaking from experience.

  11. #11
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    A thing to keep in mind is maintenace costs and reliability!

    Also look at the pro's and con's of all systems. For instance failure.

    One could imagine CO2 or NH3 system, when a component fails, the whole system could be down! The glycol system is more reliable, especially if combined with multiple chillers, either on NH3 or HFC's. The downside could be larger installation costs.

    My money is on the glycol system! I've built and serviced a lot off these without big problems and on failure of one chiller, the system can keep running!

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Quote Originally Posted by Sanderh
    My money is on the glycol system! I've built and serviced a lot off these without big problems and on failure of one Chiller, the system can keep running!
    I'm going to paraphrase your comment slightly...

    My money is on the NH3 or CO2 system! I have also been involved in both of these with no major problems. You can still keep running if one compressor fails, etc. provided you have some redundancy (similar to multiple chillers).
    If all else fails, ask for help.


  13. #13
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Quote:

    Originally Posted by: Renaud


    Some "figures" I have received for operating costs:
    Ammonia : 100%
    CO2 : 108%
    Glycol : 130%
    I wonder if the person quoting this was referring to operational costs and not installation costs.

    1. Ammonia is used as a base figure using Ammonia as a primary refrigerant circulating through the evaporators.

    2. CO2 is used as a secondary circulating refrigerant utilizing both latent and sensible cooling effects, with a small loss due to the necessary heat exchange inefficiencies.

    3. Glycol has only sensible heat transfer and therefore is less efficient by far.

    Nah... Never mind. I am not sure what the fellow is thinking. Two stage Ammonia and CO2? This doesn't make sense for meat and dairy unless you have a large frozen component. Co2 is probably not the way to go unless there are other considerations.

    I am puzzled as to what 3 systems are being suggested.

  14. #14
    Join Date
    Jun 2007
    Location
    Belgium
    Posts
    5
    Rep Power
    0

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    All cooling will be done through Ammonia. So the three systems are:
    Ammonia cooling + Ammonia circulation
    Ammonia cooling + CO2 circulation
    Ammonia cooling + Glycol circulation

    The % are OPERATING COSTS only

  15. #15
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Hi Renaud,

    I don't know in which part of the country your plant will be but in Flanders the end user will get a compensation (subsidy) from the Flemish gouvernment when using CO2/NH3 cascade.
    Take a look at :
    http://www.vlaanderen.be/ecologiepremie
    (The code for this technology is 1309).
    I'm not sure this kind of subsidy also exsist in the Walloon part of the country, but presummably it does.

    Technically I would also go for CO2/NH3.

    Best regards

  16. #16
    Join Date
    Jun 2007
    Location
    Belgium
    Posts
    5
    Rep Power
    0

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    The project would be located in Flanders so this is very interesting news for us. I can not access the ecologiepremie website before they send me a login and password by post. Do you have any idea of the importance of the premie ? % of investment or tax refund ?

  17. #17
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Hi Renaud,

    I went to check and to my surprise the 'ecologiepremie' (EP) system has been ended.
    look at : http://ewbl-publicatie.vlaanderen.be...=1155714193818
    But it seems that there is a 'light' version of this EP.
    I propose you contact de 'Vlaamse Overheid - Agentschap economie -Afdeling Economisch Ondersteuningsbeleid - Cel Ecologiepremie' :
    http://ewbl-publicatie.vlaanderen.be...=1155714193988
    Best regards
    BESC5240

  18. #18
    Join Date
    Jun 2005
    Location
    Quito
    Age
    65
    Posts
    22
    Rep Power
    0

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Dear Friend:
    1)
    Using NH3 in the evaporator is the most efficient about energy; I will use reciprocating compressors, if I believe the room cooling demand is very changing most off the time.

    If you can define some substantial minimum load use a combination screw-piston compressor system. A screw compressor with variable Vi as a base compressor to carry with the base load working from 70% to 100% of its capacity (at these capacities screw compressors have an efficiency quite as they were piston compressors). And to deal with the picks use a reciprocating compressor with discharge capacity cylinders (pistons) to carry with loads above the capacity of the screw compressor up to the maximum load
    If this is the case, I suggest to investigate the cooling load demand during a representative period of time to define time Vs load curves in order to find (or estimate) a base and maximum capacities of the compressors., and to do a detailed energy cost analysis, taking into account the load demand, the BHP, the efficiency of the compressor at the various point of the load demand curves, the energy cost, etc.
    Remember that a low initial investment could drive you to a high energy cost for the rest of the life time of the project.

    2)
    If you are very much concerned about safety or NH3 contamination risks inside the cool rooms you should use glycol (brine) in the evaporators and NH3 in the power room.
    But remember that to use a secondary refrigerant (in this case, glycol) the SST (saturated suction temperature) of the primary refrigerant (NH3) should be keep about 10F below the SST used in the case of the use off NH3 alone. This mean more energy cost. But is not that bad in the case of rooms above freezing.

    3)
    Try to do the load calculations, the load curves, the integrated time during the chosen period of time (week, month, year), define your base and pick load, the TD at your evaporators in the different rooms (the recommended TD depends on the stored goods), and give to the bidders your energy cost, the numbers of year for energy evaluation cost and as much spec as you can in order to get equivalent quotations for comparing apples with apples (not include in the bidding documentation, the installations cost, only: equipment, control panels, main valves, tanks, costly hardware). It is also important to ask for energy consumption of the system at various loads. Drive the vendors to your best system selection instead to let them impose what is best for their business
    Best Regards
    GAR&Ing.

  19. #19
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    I'm surprised the CO2 system is 8% less efficient than the pumped NH3.

    We use NH3/CO2 systems in many applications and in all cases i believe it was more efficient (plus there is the tax incentive...)

    For the 2°C rooms we use hot gas defrost at around 43BAR

    also CO2 can be used as a "volotile" secondary, giving much more duty for the refrigerant volume, and therefor much smaller/lighter pipework.

    hot gas defrost is still possible with CO2 as a secondary "volatile" fluid, plenty of heat available on the NH3 oil coolers
    Last edited by Plank!; 12-09-2007 at 10:56 PM. Reason: my spelling SUCKS

  20. #20
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Quote Originally Posted by Dan View Post
    Quote:

    Originally Posted by: Renaud

    Nah... Never mind. I am not sure what the fellow is thinking. Two stage Ammonia and CO2? This doesn't make sense for meat and dairy unless you have a large frozen component. Co2 is probably not the way to go unless there are other considerations.
    It can still be a single stage system with pumped CO2 as a volatile secondary fluid.

    The chiller/heat exchanger just has the added duty of CO2 condenser

  21. #21
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    Hi All
    I have read all the above and the company I work for have refrigerated 4 supermarket distribution warehouses using Glycol as the refrigerant in the 2, 7 and 13 degree rooms.
    The main plant is NH3 with plate heat exchangers using a closed loop Glycol circuit.
    The defrosting is done by shutting a 3 way valve and having a secondary pump and heater element and thermostat. The brine is heated during defrost and circulated through the coil.
    This system works fairly well only problem is if heaters fail or trip the coil can ice up.
    Pumped liquid NH3 is probably the best but the amount of refrigerant in the plant can large and the leak factor has to be considered.
    Hope this has helped.
    Paul

  22. #22
    Pud's Avatar
    Pud Guest

    Re: Choosing between CO2, NH3 and GLYCOL circulation

    G'Day Renaud,
    Renaud, how concerned are you about the environment?
    It seems that a cascade system using Carbon Dioxide as the primary and Ammonia as the secondary would be the most efficient and environmentally friendlly.

    Cheers Pud
    Last edited by Pud; 15-09-2007 at 11:38 AM.