    compressor icing....



    hi guyz ...

    Regarding the issues of ice buid up, I know some of u think that its a stupid question to ask ( coz no reply ). For the chilled water inlet, we are not able to reduced the water temp due to standardization in the factory itself. So pls to advise what should I do in order to eliminate the ice but at the same time without touching the chilled water supply ( 11deg C ) and also to maintain the performance ( to achieve -70deg C ).

    Pls to guide me.

    Thanx.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: compressor icing....

    Insulate the lines? use a dehumidifier? put drip try under the compressor to catch water? Pay a guy to go through and check the entire system for proper operating?

    OR You could add much more information about the problem and details, perhaps even some pictures, so we have, at the very least, a vague clue as to what your talking about!

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: compressor icing....

    Quote Originally Posted by naruto1511 View Post
    hi guyz ...

    Regarding the issues of ice buid up, I know some of u think that its a stupid question to ask ( coz no reply ).
    You closed the thread when you posted it.

    Try and reply to it your self and you will see.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Jun 2007
    Location
    Malaysia, Shah Alam
    Posts
    5
    Rep Power
    0

    Re: compressor icing....

    hi guyz ...

    1st, thanx for responding. 2nd, sorry for provide u guyz with less data. This thermal shock chamber (-180~+200) using R22 (high stage) & R23 (low stage). R22 - 8.5kg, R23 - 6kg. R22 used water condenser (chilled water; 11degC / 6bar inlet). Both compressor semi-hermetic (3.75kW). R22 high pressure running - 11~13kgf/cm2. R23 high pressure - 12~15kgf/cm2.

    The problem : ice fully covered both compressor after more than 1 day machine run.

    So I need technical advise on how to eliminate or at least reduced the ice without need to replaced the whole water supply system coz the chilled water piping is connected to the whole factory.

    Thanx.

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: compressor icing....

    Hi there,

    Did you check if there is flood back?

    I suggest that you measure the superheat and make sure that there is no liquid going into the compressors.
    If there is no flood back then there must be high humidity in the machine room which causes the frosting.

    Good luck
    Regards
    Even Einstein Asked Questions

  6. #6
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: compressor icing....

    Can R23 pull down to -180 degree C or F?
    I only know of liquid nitrogen only.

  7. #7
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: compressor icing....

    Quote Originally Posted by Cofreth View Post
    Can R23 pull down to -180 degree C or F?
    I only know of liquid nitrogen only.
    I don't think so.
    The minimum temperature should be -90°C to -100°C.
    Even Einstein Asked Questions

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: compressor icing....

    Ice or frost by itself does not indicate liquid slugging of the compressor is occurring. Ice or frost only tells you that the surface temperature is below 0°C (32°F).

    If you have a reasonable suction and discharge superheat on any compressor you can quickly find if you have liquid slugging taking place.
    Last edited by US Iceman; 07-06-2007 at 04:57 PM. Reason: spelling
    If all else fails, ask for help.


  9. #9
    Join Date
    Jun 2007
    Location
    Malaysia, Shah Alam
    Posts
    5
    Rep Power
    0

    Re: compressor icing....

    sorry again, wrongly type .... not -180 but -80..... anyway, thanx for all thoughts...

  10. #10
    Join Date
    May 2007
    Location
    Philippines
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: compressor icing....

    Please try to check also the sensor of your expansion valve. Try clean it at least with sand paper and put it back tightly as I believe it controls the opening of the orifice. Have tried it before and it works as it controls liquid refrigerant from entering the compressor. Just make it a try...

    regards,
    Rac'ers 98

  11. #11
    Join Date
    Mar 2007
    Location
    usa
    Age
    48
    Posts
    8
    Rep Power
    0

    Re: compressor icing....

    is there a water regulating valve? if so close it a little bit bring up the head pressure on high side. it just might clear up both compressors

  12. #12
    Join Date
    Aug 2007
    Location
    SOUTH AFRICA
    Posts
    8
    Rep Power
    0

    Re: compressor icing....

    At - 80 You Cannot Stp Ice Forming Unless You Re Heat. What Is The Problem?