    Called out to old Daikin Split RY125FJW1C-EO code.

    Reset unit, brought on cooling.

    Low superheat, Low LP (3 bar), Low HP (9.5 bar) R22

    6.2 amps per phase.

    Freezing up on low side outdoor unit.

    Cleaned dirty filters, no change.

    Shut HP valve to check compressor - immediately both the HP and LP dropped, re-opened valve before LP switch could open.

    Decided compressor was about to conk but now wondering if am I right. Can't think whats happened inside the compressor to cause this.

    One of two units installed 1998 in a gym running 0700-2300 every day, possibly left 24/7.

    Any comments welcome, thank you



  2. #2
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Daikin HP and LP dropping after closing HP valve

    what is your on coil and off coil air temperature? Thermostat setting etc.

  3. #3
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: Daikin HP and LP dropping after closing HP valve

    Hi

    If you mean the valves on the condensing unit, shutting the HP one will drop both pressures because its clearing the evap of refrigerant (same as a pumpdown)

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin HP and LP dropping after closing HP valve

    Hi
    Sounds like indoor unit problem causing wet operation to the compressor.
    Is the indoor unit ducted or cassette type ?
    Maybe the indoor coil is dirty or the air flow's not enough.
    If you succeed in pump down why will you change comp first !
    Be careful to take hp from the inside of the outdoor unit (not from service valve)
    rgds
    cool#9

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin HP and LP dropping after closing HP valve

    I would double check the evaporator coil.

    You say that it is a gym and by past experience I have found that coils in a disgusting state.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin - Closing Flaps
    By JamRichard in forum Air Conditioning
    Replies: 4
    Last Post: 22-02-2007, 08:24 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •