    Quest sandwich cooler evap?



    I've got a sandwich cooler who was once repaired with a grossly under sized evap that rotted out, Now I need to find the correct type for it but have zero info on the thing! No numbers Nicht!!!

    So I can give ya the dimensions: 4 to 5 feet long; ruffly three feet high and 4 feet wide; it has a top pan tray with hood of same length; but ruffly 2 feet wide.

    Currently Some one has patched in a 3K BTU/h R-134a plant, and a 1200BTU TEV and evap. way to small for that kind of duty me thinks!

    Problem was it wasn't able to keep the trays cold enough to pass HI (Health inspections) No wonder! So what is the factory evap that is supposed to be in there and what plant was shipped with the unit?

    Any help will be a life saver, thanks!



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Quest sandwich cooler evap?

    Here are some picks to help.
    Last edited by The MG Pony; 09-11-2007 at 07:01 PM.

  3. #3
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Quest sandwich cooler evap?

    and the last three
    Last edited by The MG Pony; 09-11-2007 at 07:00 PM.

  4. #4
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Quest sandwich cooler evap?

    If you were in the UK I would of said save yourself some grief and just sell the customer a new cabinet, failing that, space permitting I would size it up as I would a coldroom and select the smallest panel cooler I could or even a gravity fall coil.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Quest sandwich cooler evap?

    The thing is next to scrap yard.

  6. #6
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Quest sandwich cooler evap?

    I live and work next to one lol, makes life handy when trashing a unit after I strip out any re-usable parts. FYI it is a recycling yard to be exact.

    evap is scrap, I'm obviously not puting it back in, it was just one item on the sad list of failurs of the last repair company.

    I gues I'll be doing some sizing then, good idea.
    Last edited by The MG Pony; 31-05-2007 at 05:36 PM.

  7. #7
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Quest sandwich cooler evap?

    Well I did a load calc and assuming a 38C ambient in the kitchen (100F) it is 2.1Kw/h (7102BTU/h) load.

    They had a .9Kw(3,000BTU) plant in it with a .35Kw (1200BTU) evap!!!!!!! sade thing is it is the top hood that is 56% of the load on the machine <_< I keep teling them to insulate it any way they can!

    So I need to get a 6K btu + plant on it with matched TEV and evap All most geting cheaper to get a new one.

Similar Threads

  1. NH3 thermosiphon oil cooler
    By cygbob in forum NH3
    Replies: 38
    Last Post: 22-06-2008, 05:12 PM
  2. Thermo-syphon Oil Cooler
    By B.B. in forum Industrial
    Replies: 5
    Last Post: 31-10-2005, 01:25 PM
  3. Evap motor no come on
    By Apprentice in forum Technical Discussions
    Replies: 13
    Last Post: 04-12-2003, 04:07 PM
  4. freezer is now a cooler
    By superheat in forum Commercial
    Replies: 20
    Last Post: 18-03-2003, 12:32 PM
  5. Endless Freezer as Endless Cooler (10 door)
    By herefishy in forum Commercial
    Replies: 95
    Last Post: 17-04-2002, 12:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •