    Angry Defrost cycle Searle Evaporator



    This evaporator is serving a cold store approx 5mx5m full of frozen plane food, set point is -22C. Electric defrost.

    How often do you reckon it should be defrosting? Previously it was at 8 hours, now changed to every 4 hours but still not enough.

    Iceberg formation in process, temperature creeping up!!

    Help!



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Defrost cycle Searle Evaporator

    Every 6 hours.
    Min time 30 minutes.
    Max time 45 minutes.
    Temp termination 12 degC. (defrost probe positioned in a good place)
    Drip time 2 minutes.
    Fan start -8 degC.

    Set like this it will never ice up again. Nor will you have big frozen droplets on the roof.

    Make sure you heaters are in the correct place.


    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Defrost cycle Searle Evaporator

    Contactor,

    I would say that if a defrost every 4 hours is not enough then you have another problem.

    Start with the basics, Is the door being kept shut or is the site in and out all the time, if the later are there any door strips on it or an air blower above the door ?

    now assuming the door is being kept shut, Is the unit getting enough defrost, are all the heaters working, is the drain heater working and the drain line clear.
    How is the defrost controllled, Is in on time/ termination temp or both (Is it on an eliwell/lae etc) . Is the termination probe (Probe 2) in the right place or getting a poor reading.

    Any info on the set up you can give would be a help, its one of these difficult ones to try and diagnose on the end of a PC but i hope something here may help and if you can post the other settings we should be able to sort it

    Regards

    Raymond

  4. #4
    Join Date
    Sep 2006
    Location
    Londrina
    Age
    59
    Posts
    20
    Rep Power
    0

    Re: Defrost cycle Searle Evaporator

    hi will be that valvula of expansion this very opened? , the people entran with much frequencia?

  5. #5
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Defrost cycle Searle Evaporator

    Hi Contactor,

    Check what rdocwra said.

    In my opinion defrost time and duration has no general rules and it depends on the application.
    If door is opened too many times and the outside air is moist then the defrost time would be different.
    In blast freezers where fresh fish is being frozen (generally on the ships) then after half an hour the whole coil will be frosted up and needs defrost. You see it depends on application and also the product being stored.

    You have to estimate the time and duration of defrost by experiment for each application.

    Good luck
    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Efficiency of compressor assisted HRV
    By montreal in forum Heat Pumps
    Replies: 46
    Last Post: 27-08-2007, 08:51 PM
  2. Searle Evaporator Heaters
    By Abe in forum Commercial
    Replies: 14
    Last Post: 31-12-2005, 10:24 AM
  3. Servicing Supermarket Reach-in Freezers
    By shogun7 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 30-04-2004, 12:05 AM
  4. Searle Evaporator
    By Abe in forum Commercial
    Replies: 1
    Last Post: 07-12-2002, 11:59 AM
  5. Iced Evaporator
    By Abe in forum Commercial
    Replies: 13
    Last Post: 06-11-2002, 01:34 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •