31-07-2002, 07:59 AM #1
chilled water PHE
all dears.
good day
may you all please get me some suggessions for the following?
i have installed one PHE for chilled water generation and it was running fantastic for last 8 months .
but for last few days it is not giving proper and of course rated parameters.
the details of the PHE are as follows.
alfa laval PHE ( semiwelded NH3 to water application)
125 TR at the rate of 50 CMH and
water in = +8 Deg C
water out = + 2 Deg C
EPR of danfoss is installed to control the evaporation temp. at -1 Deg C
no oil is stuck in the phe or the surge drum.
compressor is giving a capacity of 133 TR at - 1 to +40 Deg C
the problem i am facing is
even the EPR is there ,the evaporation temp. is falling down to
-10 Deg C which i fear will cause the water to frost in side of the plates and will crack the plates.
i have carried the following activities.
1.cleaned the filter of the EPR
2.replaced the CVP
3.drained out the oil; but didnt get any oil trace in side of the system
i am expecting smoe kind of suggessssions from you experts.
have a nice time ever.
waiting eagerly,
priti
-
31-07-2002, 08:25 PM #2
Hi, Priti,
Just I few quick sugestions.
1/Refrigerant charge
2/Expansion valve/level control problem
3/Reduced water flow due to dirt blocking a pump strainer
4/Damaged pumped.
I would try to establish pump flow rates on the Glycol/Brine side. If you have a flow meter on your system this is very simple, otherwise you are depending on commisioning data, such as temps in and out of the chiller and pump Amperes.
Regards. Andy.
Similar Threads
-
Do I need a chilled water buffer vessel
By Consultant in forum CommercialReplies: 32Last Post: 02-03-2011, 09:40 AM -
Chilled Water Coil
By elmusasc in forum FundamentalsReplies: 4Last Post: 11-08-2006, 02:42 PM -
chilled water pump design
By afeef in forum FundamentalsReplies: 5Last Post: 16-09-2005, 12:06 AM -
chilled water storage tank!
By dchatta in forum Technical DiscussionsReplies: 4Last Post: 24-05-2004, 04:23 PM -
Refrigerant vs Chilled Water
By baker in forum Air ConditioningReplies: 4Last Post: 16-01-2004, 02:17 PM