    chilled water PHE



    all dears.
    good day

    may you all please get me some suggessions for the following?

    i have installed one PHE for chilled water generation and it was running fantastic for last 8 months .

    but for last few days it is not giving proper and of course rated parameters.

    the details of the PHE are as follows.

    alfa laval PHE ( semiwelded NH3 to water application)
    125 TR at the rate of 50 CMH and
    water in = +8 Deg C
    water out = + 2 Deg C
    EPR of danfoss is installed to control the evaporation temp. at -1 Deg C
    no oil is stuck in the phe or the surge drum.
    compressor is giving a capacity of 133 TR at - 1 to +40 Deg C

    the problem i am facing is
    even the EPR is there ,the evaporation temp. is falling down to
    -10 Deg C which i fear will cause the water to frost in side of the plates and will crack the plates.

    i have carried the following activities.
    1.cleaned the filter of the EPR
    2.replaced the CVP
    3.drained out the oil; but didnt get any oil trace in side of the system

    i am expecting smoe kind of suggessssions from you experts.

    have a nice time ever.

    waiting eagerly,

    priti



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi, Priti,
    Just I few quick sugestions.

    1/Refrigerant charge
    2/Expansion valve/level control problem
    3/Reduced water flow due to dirt blocking a pump strainer
    4/Damaged pumped.

    I would try to establish pump flow rates on the Glycol/Brine side. If you have a flow meter on your system this is very simple, otherwise you are depending on commisioning data, such as temps in and out of the chiller and pump Amperes.
    Regards. Andy.

Similar Threads

  1. Do I need a chilled water buffer vessel
    By Consultant in forum Commercial
    Replies: 32
    Last Post: 02-03-2011, 10:40 AM
  2. Chilled Water Coil
    By elmusasc in forum Fundamentals
    Replies: 4
    Last Post: 11-08-2006, 02:42 PM
  3. chilled water pump design
    By afeef in forum Fundamentals
    Replies: 5
    Last Post: 16-09-2005, 12:06 AM
  4. chilled water storage tank!
    By dchatta in forum Technical Discussions
    Replies: 4
    Last Post: 24-05-2004, 04:23 PM
  5. Refrigerant vs Chilled Water
    By baker in forum Air Conditioning
    Replies: 4
    Last Post: 16-01-2004, 03:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •