    Pressure loss versus speed in suction line



    Would like your opinion on this: when calculating a suction line, we must take in account a certain speed to ensure oil return (I take 8 m/s or 26ft/s) and a max allowable pressure drop of 2K.
    What if you have a long line and speed is already at it's minimum (5 m/s or 16 ft/s) but max allowable pressure drop is 4K?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure loss versus speed in suction line

    Sorry forgot, my opinion on this is that the oil return is the determining factor, so the speed must stay above min allowable speed.
    Pressure drop will give bigger losses but better this then oil staying in the circuit.

    One of my students asked me a smart question: suppose a hypothectical system wit a pressure drop of 6 K along the suction line. Waht pressure or temeprature does he need to take to calculate the suction line? The evaporating pressure in teh evaporator or the pressure measured at the compressor inlet?
    Last edited by Peter_1; 26-05-2007 at 07:55 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Pressure loss versus speed in suction line

    Quote Originally Posted by Peter_1 View Post
    Would like your opinion on this: when calculating a suction line, we must take in account a certain speed to ensure oil return (I take 8 m/s or 26ft/s) and a max allowable pressure drop of 2K.
    What if you have a long line and speed is already at it's minimum (5 m/s or 16 ft/s) but max allowable pressure drop is 4K?
    Hi Peter 1

    Get an oil sep on it quick.

    Regards
    Lrac

  4. #4
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Pressure loss versus speed in suction line

    Quote Originally Posted by LRAC View Post
    Hi Peter 1

    Get an oil sep on it quick.

    Regards
    Lrac
    LOL... you should know Peter better by now.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pressure loss versus speed in suction line

    Quote Originally Posted by Peter_1
    What pressure or temperature does he need to take to calculate the Suction Line? The evaporating pressure in the Evaporator or the pressure measured at the Compressor inlet?
    Since one of your concerns is the compressor capacity I say you should use the evaporating pressure. The evaporator capacity is based on the rating per degree of temperature difference.

    Therefore, the total evaporator capacity is Q (kW/° or BTUH/°) X TD (°K or °F). The TD determines the evaporating temperature and pressure.

    The suction line pressure loss determines the compressor suction pressure (& saturated temperature). This is one of the required operating conditions to find the compressor capacity so that it matches the evaporator capacity.

    With this method you always know what the compressor is supposed to be operating at.

    Quote Originally Posted by Peter_1
    my opinion on this is that the oil return is the determining factor, so the speed must stay above min allowable speed.
    I agree. This is one of the penalties for operating a "*****" system. However, the problem is increased when the compressor has capacity control. In this case, you have additional concerns.
    If all else fails, ask for help.


  6. #6
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Pressure loss versus speed in suction line

    Hi Peter,

    As far as I have read, the minimum velocity for oil return in horizontal pipe is 2.5m/s (of course with a 1% slope to wards the compressor).
    And for vertical risers the minimum velocity is 5m/s.
    I think if ASHRAE tables are used then, they are calculated for those velocities.

    For the pressure I think we must take the compressor suction pressure because this is the actual inlet pressure which compressor takes. It is obvious on a P-h diagram. This is why compressor capacity decreases with high suction pressure drop.

    Cheers
    Even Einstein Asked Questions

  7. #7
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Pressure loss versus speed in suction line

    I consider the mini-velocities of refrigrant are determined by different tubes' figuration, refrigrants and compressor types. 2.5 m/s in horizontal pipe is not safe enough for oil return, 4 m/s may be better in normal feron system.
    "Therefore, the total Evaporator capacity is Q (kW/° or BTUH/°) X TD (°K or °F). The TD determines the evaporating temperature and pressure."
    Iceman, your words make me confusedly. Theoretically, cooling capacity is determined by the latent heat quantity under the definite evap pressure, refrigerant flux; it also can be caculated by TD X K(heat exchange ration) X heat transfer Face, but I can't agree with your last expression, I think the pressure determines phase transition temperature/evap temp, the TD determines the Cooling Capacity.
    Last edited by Peter_1; 28-05-2007 at 08:09 AM.

  8. #8
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Pressure loss versus speed in suction line

    Hi There,

    The paragraph below is taken from Mcquay Refrigerant Piping Design Guide.

    Piping Design Basics


    Good piping design results in a balance between the initial cost, pressure drop, and system
    reliability. The initial cost is impacted by the diameter and layout of the piping. The pressure drop
    in the piping must be minimized to avoid adversely affecting performance and capacity. Because
    almost all field-piped systems have compressor oil passing through the refrigeration circuit and back
    to the compressor, a minimum velocity must be maintained in the piping so that sufficient oil is
    returned to the compressor sump at full and part load conditions. A good rule of thumb is a
    minimum of:


    500 feet per minute (fpm) or 2.54 meters per second (mps) for horizontal suction and hot
    gas lines

    1000 fpm (5.08 mps) for suction and hot gas risers

    Less than 300 fpm (1.54 mps) to avoid liquid hammering from occurring when the solenoid
    closes on liquid lines
    Hard drawn copper tubing is used for halocarbon refrigeration systems. Types L and K are approved


    Cheers
    Even Einstein Asked Questions

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Pressure loss versus speed in suction line

    Lana, if I can go as low as 500fpm, then my problem is solved of course.

    But you are speaking about compressor suction pressure and US Iceman is speaking about evaporator suction pressure. This is of course not a big difference but it's worth making once the exercise.
    I think that pure theoretically that the tube must gradually expand the more we approach the compressor.
    So starting with a small tube at the evaporator outlet and expanding towards the compressor.

    PS: Ispell is saying that 'towards' is wrong. What's the correct expression then?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Pressure loss versus speed in suction line

    Hi Peter,

    PS: Ispell is saying that 'towards' is wrong. What's the correct expression then?
    I had the same warning. I don't know. We understand each other, whatever Ispell says .
    I think this is one of the words which does not need "s" at the end.

    Cheers
    Last edited by lana; 28-05-2007 at 02:01 PM.
    Even Einstein Asked Questions

  11. #11
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Pressure loss versus speed in suction line

    Quote Originally Posted by Peter_1 View Post
    So starting with a small tube at the evaporator outlet and expanding towards the compressor.

    PS: Ispell is saying that 'towards' is wrong. What's the correct expression then?

    I think that the term would be expand away from the evap?
    Not sure!!
    But like you stated we all knew what you meant .

    Cheers taz.

  12. #12
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Pressure loss versus speed in suction line

    Hi Peter,

    The following text is from ASHRAE Refrigeration handbook (chapter 2) :

    A pressure drop in the suction line reduces a system’s capacity because it forces the compressor to operate at a lower suction pressure to maintain a desired evaporating temperature in the coil. The suction line is normally sized to have a pressure drop from friction no greater than the equivalent of about a 1 K change in saturation temperature.
    Hope this helps.

    BTW : about the word "towards" , I found out that "toward" is American English and "towards" is British. SO Ispell is American .....
    I like British one, I am little bit of Anglo-Saxon .

    Cheers
    Even Einstein Asked Questions

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pressure loss versus speed in suction line

    ernestlin,

    Here in the US an air-cooling evaporator used in refrigeration applications is rated based on BTUH/°F of temperature difference (TD).

    The entering air temperature to the evaporator is considered the room temperature, therefore room air temperature - TD = evaporating temperature.

    The TD fixes the the evaporating temperature, which in turn determines the evaporating pressure for a specific refrigerant.

    Therefore, if you take the evaporating temperature - the equivalent temperature loss of the suction line you have the saturated suction temperature of the compressor.

    The important issue to remember is not whether you use the suction pressure or the evaporating pressure, but to make sure you include the suction line pressure loss so that it does not affect the system capacity.

    If you select the compressor based only on evaporating temperature, the evaporator TD will re-balance at a lower TD and loose evaporator capacity...

    Quote Originally Posted by Peter_1
    I think that pure theoretically that the tube must gradually expand the more we approach the compressor.
    Theoretically, I agree. Although I do not do this. What you are describing Peter is similar to designing air duct work for a constant static pressure loss.

    In horizontal lines I would rather have them sloped back to the compressor, but large enough for minimum pressure loss. But, I also look at the minimum velocities as a comparison.

    The way I look at this problem is to carefully evaluate the risers and use of traps to get the oil back into a horizontal line back to the compressor.

    Once the oil is in the horizontal line, most of the problems are solved anyway.
    If all else fails, ask for help.


  14. #14
    Join Date
    May 2006
    Location
    china
    Posts
    98
    Rep Power
    18

    Re: Pressure loss versus speed in suction line

    Hi, Iceman, I got your point, we just look at this issue from a different angle, for design or selection, TD always is a specific empiric value, right?
    Lana, your datum is right, but mine isn't incorrect, it comes from tecumesh's guide manual. For various consideration, different Co. may afford different values, they're all based on expriments.

  15. #15
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Pressure loss versus speed in suction line

    Hi ernestlin,

    Lana, your datum is right, but mine isn't incorrect, it comes from tecumesh's guide manual. For various consideration, different Co. may afford different values, they're all based on expriments
    I didn't say your values are incorrect. I was talking about the "minimum" velocities. Any velocities above those values would be more than safe.

    Cheers
    Even Einstein Asked Questions

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. propane compressor suction drum
    By Ahmed_LNG in forum Refrigerants
    Replies: 7
    Last Post: 01-01-2006, 08:01 AM
  3. Measure suction line pressure drop with thermometer
    By Steve Wright in forum Fundamentals
    Replies: 7
    Last Post: 17-09-2005, 11:05 PM
  4. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •