Thread: Mycom N8wb
    Mar 2007
    jakarta
    49
    30
    Mycom N8wb
    Dear guys,
    I have problem that compressor damage (see attch. file). Here iis my suspect is lubrication failure, thats no oil pressure to compressor, oil pressure switch not working and compressor still in running and cause the parts melting.
    There is anybody have an opinion about this matter? how about dirty oil (sludge or gram) could cloge the oil line or oil hole at the parts while compressor running? is it possible?
    Thank you
    Faryuki
    Attached Files Attached Files
    Jul 2006
    73
    865
    26
    Re: Mycom N8wb
    Fariuki;
    It may be too late to tell.
    Oil pressure failure may be one explanation. I have seen similar damage from loss of cooling water. One customer had a B machine running NH3 that lost cooling water and the machine was so badly damaged throughout that if we had not known the source of the problem to begin with we would have not been able to sort it out.
    After you repair or replace the machine test all the safeties, especially the oil pressure failure. I have seen them miswired in such a manner that they would not operate when the machine was running. It tested fine when the disconnect was pulled to the motor, it was of no use when the mag was pulled in.
    Consider installing a high discharge temperature cutout if one was not fitted.
    Mar 2006
    Norfolk
    160
    Re: Mycom N8wb
    Looks very much like an oil failure problem - oil pressure switch not working was not good.
    Check pump filters and lines, it is a bit too late to sample the oil as it will be contaminated with the debris from the failure.
    Paula
    Mar 2007
    jakarta
    49
    30
    Re: Mycom N8wb
    OKe,
    thank you for the advise..
    many thanks
    Faryuki
    malaysia
    159
    Re: Mycom N8wb
    Quote Originally Posted by faryuki View Post
    Dear guys,
    Thank you
    Faryuki
    faryuki,
    it looks to me that you are either a mycom technician or mycom contractor.
    anyway, mycom has common problems like yours all over.
    it could be oil sep issue or liquid floodback.
    lee,malaysia.
  1. Mycom 250VLD
    By nh3wizard in forum NH3
    Last Post: 14-08-2008, 06:37 PM
  2. Mycom 160lud
    By DSK in forum Industrial Compressors
    Last Post: 15-12-2007, 06:47 PM
  3. Replies: 7