    Chilld Water To Evaporator Coil



    HAI SAIRS,
    one water cooler having 20 ltr/h capacity. If i try it to reduce water quantity to 2 ltr,this water suplied to 1.5 ton evaporator coil and work with normal fan cfm over it , what was the after effect of this system . Expect detail reply please.



  2. #2
    Join Date
    Oct 2005
    Location
    IRAN
    Age
    53
    Posts
    878
    Rep Power
    19

    Re: Chilld Water To Evaporator Coil

    Hi there,

    If you reduce water flow rate then water velocity inside the tubes will be less than before and the heat transfer rate will be much less.
    I would not advise this because the coil performance will be reduced considerably.

    Give more info so someone here can help you.
    Cheers
    Even Einstein Asked Questions

  3. #3
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Smile Re: Chilld Water To Evaporator Coil

    Quote Originally Posted by jaison View Post
    HAI SAIRS,
    one water cooler having 20 ltr/h capacity. If i try it to reduce water quantity to 2 ltr,this water suplied to 1.5 ton evaporator coil and work with normal fan cfm over it , what was the after effect of this system . Expect detail reply please.
    Hi Jaison

    If the water capacity (flow rate) is reduced the exit temperature form the chiller will be definitely dropped and may be reached to a freezing point inside the tubes. however, the amount heat capacity which will be removed from the chilled water will actually be decreased as a result of the drop occurred in the overall heat transfer coefficient (Lessing in water mean velocity) as Lana said. This will lead to a deficiency in cooling coil (fan-coil) performance (decline in removal heat from the unconditioned air ) in term of the sensible and latent removal heat from the unconditioned air. In addition, the chiller itself will suffer from drop in its COP as a result of the drop occurred in evaporator performances (Lower TEV).

    kind regards

    Mohamed

  4. #4
    Join Date
    Mar 2006
    Location
    Malaysia
    Age
    48
    Posts
    233
    Rep Power
    19

    Smile Re: Chilld Water To Evaporator Coil

    Quote Originally Posted by jaison View Post
    HAI SAIRS,
    one water cooler having 20 ltr/h capacity. If i try it to reduce water quantity to 2 ltr,this water suplied to 1.5 ton evaporator coil and work with normal fan cfm over it , what was the after effect of this system . Expect detail reply please.
    Hi Jaison

    If the water capacity (flow rate) is reduced the exit water temperature form the chiller will be definitely dropped and may be reached to a freezing point inside the tubes. However, the amount of heat capacity which will be removed from the chilled water will actually be decreased as a result of the drop occurred in the overall heat transfer coefficient (Lessing in water mean velocity) as Lana said. This will lead to a deficiency in cooling coil (fan-coil) performance (decline in removal heat from the unconditioned air ) in terms of the sensible and latent removal heat from the unconditioned air. In addition, the chiller itself will suffer from drop in its COP as a result of the drop occurred in evaporator performances (Lower TEV).

    kind regards

    Mohamed

  5. #5
    Join Date
    Mar 2007
    Location
    uae
    Age
    44
    Posts
    24
    Rep Power
    0

    Re: Chilld Water To Evaporator Coil

    I meaned that , i want to make small airconditioner by means of chiller method.I choose one water cooler about 20 ltr/h , but water quantity reduced to according to 1.5 ton air handlig unit. a small pump used to circulate water from the tank.How it will work? give me more idea about it.If we put salt water on the tank what effect will get?.

  6. #6
    Join Date
    May 2007
    Location
    Belgium
    Age
    51
    Posts
    87
    Rep Power
    18

    Re: Chilld Water To Evaporator Coil

    Jaison, you could use a (relatively large) storage tank, to avoid the negative effects Mohamed and Lana correclty described. That is, if you use two separate pumps (one 20ltr for loop between chiller and storage, one to feed the indoor unit coil).

    Still, the capacity of your indoor unit at 2 ltr/ hour (you could use a condensate removal pump?) would be, euhm, neglectible. You'd be better off buying a chinese portable unit - the do not cool either, but are a lot cheaper and easier to install .

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •